Hello,
I have a question on an InstaSPIN-FOC Lab project in motorware.
Particularly it is on Lab 11a.
A code snippet in mainISR() is as follows:
// when appropriate, run the PID speed controller
if((pidCntSpeed++ >= USER_NUM_CTRL_TICKS_PER_SPEED_TICK) && (!gMotorVars.Flag_enableRsRecalc))
{
.........................................
// run speed controller
PID_run_spd(pidHandle[0],TRAJ_getIntValue(trajHandle_spd),speed_pu,&(gIdq_ref_pu.value[1]));
}
Because of "&& (!gMotorVars.Flag_enableRsRecalc)" in the if statement, the PID speed controller may not be run if the Rs online recalibration function is enabled.
In other words, the Rs online recalibration function may have to be disabled if the PID speed controller can be run in Lab 11a.
Am I correct?
Thank you for your guidance.
With regards,
JS Yoo
Flag_enableRsRecalc is not for Rs online calibration, it's for Rs re-calculation before startup that the motor is stalled without speed control.