MSP430F6779A SVM interrupt only happens once
Other Parts Discussed in Thread: MSP430F6779A
I setup the SVM on the MSP430F6779A to give an interrupt if the supply voltage drops below 2.9V. as shown below:
//unlock PMM
  PMMCTL0_H=PMMPW_H;
  //check voltage level
  switch(PMMCTL0&PMMCOREV_3){
    //settings for highest core voltage settings
    case PMMCOREV_3:
      //setup high side supervisor and monitor
      SVSMHCTL=SVMHE|SVSHE|SVSHRVL_3|SVSMHRRL_7;
    break;
  //clear interrupt flags
  PMMIFG&=~(SVMLIFG|SVMHIFG|SVMHVLRIFG|SVMLVLRIFG);
  //setup interrupts
  PMMRIE|=SVMLIE|SVMHIE|SVMHVLRIE|SVMLVLRIE;
  //lock PMM
  PMMCTL0_H=0;
In the SYSNMI_VECTOR I set a flag for software if I see the low voltage interrupts from the SVM when the voltage comes back up I clear the flags from the module:
//================[System NMI Interrupt]=========================
void SYS_NMI(void)__ctl_interrupt[SYSNMI_VECTOR]{
  switch(SYSSNIV){
    //core supply voltage monitor interrupt
    case SYSSNIV_SVMLIFG:
      //event to report error
      //set flag
    break;
    //input supply voltage monitor interrupt
    case SYSSNIV_SVMHIFG:
      //set flag
    break;
    //core supply voltage monitor delay interrupt
    case SYSSNIV_DLYLIFG:
    break;
    //interrupt supply voltage monitor delay interrupt
    case SYSSNIV_DLYHIFG:
    break;
    //Vacant memory access interrupt
    case SYSSNIV_VMAIFG:
    break;
    //JTAG mailbox in interrupt
    case SYSSNIV_JMBINIFG:
    break;
    //JTAG mailbox out interrupt
    case SYSSNIV_JMBOUTIFG:
    break;
    //SVMLVLRIFGSVMHVLRIFG
    case SYSSNIV_VLRLIFG:
      //clear interrupt flag bits
      //unlock PMM
      PMMCTL0_H=PMMPW_H;
      PMMIFG&=~(SVMLIFG|SVMLVLRIFG);
      //lock PMM
      PMMCTL0_H=0;
    break;
    //SVMHVLRIFGSVMHVLRIFG
    case SYSSNIV_VLRHIFG:
      //unlock PMM
      PMMCTL0_H=PMMPW_H;
      PMMIFG&=~(SVMHIFG|SVMHVLRIFG);
      //lock PMM
      PMMCTL0_H=0;
    break;
When the voltage is lowered below about 3V I see the flag from the interrupt. If I bring the voltage back up to 3.3V and then down again I do not get any more interrupts. If I take the voltage all the way down to 2V the MSP resets and doesn't come on until the voltage raises above 3V. Is there something I need to do to get multiple SVM interrupts or do I have to reset when this happens?
  • Hi Jesse,
    Can you take screen shots of the the SVSSNIV and PMMIFG registers' contents before and after the 1st, 2nd, and 3rd time you cross the SVMH thresholds?
    Cameron
  • I dumped the registers from the SVS and PMM as shown below. I first paused after the registers were configured.
    PMM
        PMMCTL0              0x9603
            PMMCOREV         3
            PMMSWBOR         0
            PMMSWPOR         0
            PMMSREGOFF       0
            PMMHPMRE         0
            PMMKEY           0x96
        PMMCTL1              0x0000
            PMMREFMD         0
            PMMREFACC        0
            PMMCMD           0x0
        SVSMHCTL             0x4707
            SVSMHRRL         0x7
            SVSMHDLYST       0
            SVSHMD           0
            SVSMHEVM         0
            SVSMHACE         0
            SVSHRVL          0x3
            SVSHE            1
            SVSHFP           0
            SVMHOVPE         0
            SVMHE            1
            SVMHFP           0
        SVSMLCTL             0b0100011100000011
            SVSMLRRL         0x3
            SVSMLDLYST       0
            SVSLMD           0
            SVSMLEVM         0
            SVSMLACE         0
            SVSLRVL          0x3
            SVSLE            1
            SVSLFP           0
            SVMLOVPE         0
            SVMLE            1
            SVMLFP           0
        SVSMIO               0x0020
            SVSLEVE          0
            SVMLEVE          0
            SVMLOE           0
            SVMLVRLOE        0
            SVMOUTPOL        1
            SVSHEVE          0
            SVMHEVE          0
            SVMHOE           0
            SVMHVRLOE        0
        PMMIFG               0x0010
            SVSMLDLYIFG      0
            SVMLIFG          0
            SVMLVLRIFG       0
            SVSMHDLYIFG      1
            SVMHIFG          0
            SVMHVLRIFG       0
            PMMBORIFG        0
            PMMRSTIFG        0
            PMMPORIFG        0
            SVSHIFG          0
            SVSLIFG          0
            PMMRSTLPM5IFG    0
        PMMRIE               0x1166
            SVSMLDLYIE       0
            SVMLIE           1
            SVMLVLRIE        1
            SVSMHDLYIE       0
            SVMHIE           1
            SVMHVLRIE        1
            SVSLPE           1
            SVMLVLRPE        0
            SVSHPE           1
            SVMHVLRPE        0
        PM5CTL0              0x0000
            LOCKLPM5         0
    SYS
        SYSCTL               0x0000
            SYSRIVECT        0
            SYSPMMPE         0
            SYSBSLIND        0
            SYSJTAGPIN       0
        SYSBSLC              0x8003
            SYSBLSIZE        3
            SYSBSLR          0
            SYSBSLOFF        0
            SYSBSLPE         1
        SYSJMBC              0x000c
            JMBIN0FG         0
            JMBIN1FG         0
            JMBOUT0FG        1
            JMBOUT1FG        1
            JMBMODE          0
            JMBCLR0OFF       0
            JMBCLR1OFF       0
        SYSJMBI0             0x0110
        SYSJMBI1             0xffff
        SYSJMBO0             0x0000
        SYSJMBO1             0x0000
        SYSBERRIV            0x0000
        SYSUNIV              0x0000
            SYSUNVEC         0
        SYSSNIV              0x0000
            SYSNVEC          0
        SYSRSTIV             0x0000
            SYSRSTVEC        0
    Then I lowered the voltage to about 2.99V until I got the interrupt from the PMM and dumped the registers again:
    PMM
        PMMCTL0              0x9603
            PMMCOREV         3
            PMMSWBOR         0
            PMMSWPOR         0
            PMMSREGOFF       0
            PMMHPMRE         0
            PMMKEY           0x96
        PMMCTL1              0x0000
            PMMREFMD         0
            PMMREFACC        0
            PMMCMD           0x0
        SVSMHCTL             0x4707
            SVSMHRRL         0x7
            SVSMHDLYST       0
            SVSHMD           0
            SVSMHEVM         0
            SVSMHACE         0
            SVSHRVL          0x3
            SVSHE            1
            SVSHFP           0
            SVMHOVPE         0
            SVMHE            1
            SVMHFP           0
            SVSMLRRL         0x3
            SVSMLDLYST       0
            SVSLMD           0
            SVSMLEVM         0
            SVSMLACE         0
            SVSLRVL          0x3
            SVSLE            1
            SVSLFP           0
            SVMLOVPE         0
            SVMLE            1
            SVMLFP           0
        SVSMIO               0x0020
            SVSLEVE          0
            SVMLEVE          0
            SVMLOE           0
            SVMLVRLOE        0
            SVMOUTPOL        1
            SVSHEVE          0
            SVMHEVE          0
            SVMHOE           0
            SVMHVRLOE        0
        PMMIFG               0x0010
            SVSMLDLYIFG      0
            SVMLIFG          0
            SVMLVLRIFG       0
            SVSMHDLYIFG      1
            SVMHIFG          0
            SVMHVLRIFG       0
            PMMBORIFG        0
            PMMRSTIFG        0
            PMMPORIFG        0
            SVSHIFG          0
            SVSLIFG          0
            PMMRSTLPM5IFG    0
        PMMRIE               0x1146
            SVSMLDLYIE       0
            SVMLIE           1
            SVMLVLRIE        1
            SVSMHDLYIE       0
            SVMHIE           0
            SVMHVLRIE        1
            SVSLPE           1
            SVMLVLRPE        0
            SVSHPE           1
            SVMHVLRPE        0
        PM5CTL0              0x0000
            LOCKLPM5         0
    SYS
        SYSCTL               0x0000
            SYSRIVECT        0
            SYSPMMPE         0
            SYSBSLIND        0
            SYSJTAGPIN       0
        SYSBSLC              0x8003
            SYSBLSIZE        3
            SYSBSLR          0
            SYSBSLOFF        0
            SYSBSLPE         1
        SYSJMBC              0x000c
            JMBIN0FG         0
            JMBIN1FG         0
            JMBOUT0FG        1
            JMBOUT1FG        1
            JMBMODE          0
            JMBCLR0OFF       0
            JMBCLR1OFF       0
        SYSJMBI0             0x0110
        SYSJMBI1             0xffff
        SYSJMBO0             0x0000
        SYSJMBO1             0x0000
        SYSBERRIV            0x0000
        SYSUNIV              0x0000
            SYSUNVEC         0
        SYSSNIV              0x0000
            SYSNVEC          0
        SYSRSTIV             0x0000
            SYSRSTVEC        0
    I then set the voltage back up to 3.3V and read the registers again:
    PMM
        PMMCTL0              0x9603
            PMMCOREV         3
            PMMSWBOR         0
            PMMSWPOR         0
            PMMSREGOFF       0
            PMMHPMRE         0
            PMMKEY           0x96
        PMMCTL1              0x0000
            PMMREFMD         0
            PMMREFACC        0
            PMMCMD           0x0
        SVSMHCTL             0x4707
            SVSMHRRL         0x7
            SVSMHDLYST       0
            SVSHMD           0
            SVSMHEVM         0
            SVSMHACE         0
            SVSHRVL          0x3
            SVSHE            1
            SVSHFP           0
            SVMHOVPE         0
            SVMHE            1
            SVMHFP           0
            SVSMLRRL         0x3
            SVSMLDLYST       0
            SVSLMD           0
            SVSMLEVM         0
            SVSMLACE         0
            SVSLRVL          0x3
            SVSLE            1
            SVSLFP           0
            SVMLOVPE         0
            SVMLE            1
            SVMLFP           0
        SVSMIO               0x0020
            SVSLEVE          0
            SVMLEVE          0
            SVMLOE           0
            SVMLVRLOE        0
            SVMOUTPOL        1
            SVSHEVE          0
            SVMHEVE          0
            SVMHOE           0
            SVMHVRLOE        0
        PMMIFG               0x0030
            SVSMLDLYIFG      0
            SVMLIFG          0
            SVMLVLRIFG       0
            SVSMHDLYIFG      1
            SVMHIFG          1
            SVMHVLRIFG       0
            PMMBORIFG        0
            PMMRSTIFG        0
            PMMPORIFG        0
            SVSHIFG          0
            SVSLIFG          0
            PMMRSTLPM5IFG    0
        PMMRIE               0x1146
            SVSMLDLYIE       0
            SVMLIE           1
            SVMLVLRIE        1
            SVSMHDLYIE       0
            SVMHIE           0
            SVMHVLRIE        1
            SVSLPE           1
            SVMLVLRPE        0
            SVSHPE           1
            SVMHVLRPE        0
        PM5CTL0              0x0000
            LOCKLPM5         0
    SYS
        SYSCTL               0x0000
            SYSRIVECT        0
            SYSPMMPE         0
            SYSBSLIND        0
            SYSJTAGPIN       0
        SYSBSLC              0x8003
            SYSBLSIZE        3
            SYSBSLR          0
            SYSBSLOFF        0
            SYSBSLPE         1
        SYSJMBC              0x000c
            JMBIN0FG         0
            JMBIN1FG         0
            JMBOUT0FG        1
            JMBOUT1FG        1
            JMBMODE          0
            JMBCLR0OFF       0
            JMBCLR1OFF       0
        SYSJMBI0             0x0110
        SYSJMBI1             0xffff
        SYSJMBO0             0x0000
        SYSJMBO1             0x0000
        SYSBERRIV            0x0000
        SYSUNIV              0x0000
            SYSUNVEC         0
        SYSSNIV              0x0000
            SYSNVEC          0
        SYSRSTIV             0x0000
            SYSRSTVEC        0
    I then lowered the voltage to around 2.5V and got no interrupt. Registers are below:
    PMM
        PMMCTL0              0x9603
            PMMCOREV         3
            PMMSWBOR         0
            PMMSWPOR         0
            PMMSREGOFF       0
            PMMHPMRE         0
            PMMKEY           0x96
        PMMCTL1              0x0000
            PMMREFMD         0
            PMMREFACC        0
            PMMCMD           0x0
        SVSMHCTL             0x4707
            SVSMHRRL         0x7
            SVSMHDLYST       0
            SVSHMD           0
            SVSMHEVM         0
            SVSMHACE         0
            SVSHRVL          0x3
            SVSHE            1
            SVSHFP           0
            SVMHOVPE         0
            SVMHE            1
            SVMHFP           0
            SVSMLRRL         0x3
            SVSMLDLYST       0
            SVSLMD           0
            SVSMLEVM         0
            SVSMLACE         0
            SVSLRVL          0x3
            SVSLE            1
            SVSLFP           0
            SVMLOVPE         0
            SVMLE            1
            SVMLFP           0
        SVSMIO               0x0020
            SVSLEVE          0
            SVMLEVE          0
            SVMLOE           0
            SVMLVRLOE        0
            SVMOUTPOL        1
            SVSHEVE          0
            SVMHEVE          0
            SVMHOE           0
            SVMHVRLOE        0
        PMMIFG               0x0030
            SVSMLDLYIFG      0
            SVMLIFG          0
            SVMLVLRIFG       0
            SVSMHDLYIFG      1
            SVMHIFG          1
            SVMHVLRIFG       0
            PMMBORIFG        0
            PMMRSTIFG        0
            PMMPORIFG        0
            SVSHIFG          0
            SVSLIFG          0
            PMMRSTLPM5IFG    0
        PMMRIE               0x1146
            SVSMLDLYIE       0
            SVMLIE           1
            SVMLVLRIE        1
            SVSMHDLYIE       0
            SVMHIE           0
            SVMHVLRIE        1
            SVSLPE           1
            SVMLVLRPE        0
            SVSHPE           1
            SVMHVLRPE        0
        PM5CTL0              0x0000
            LOCKLPM5         0
    SYS
        SYSCTL               0x0000
            SYSRIVECT        0
            SYSPMMPE         0
            SYSBSLIND        0
            SYSJTAGPIN       0
        SYSBSLC              0x8003
            SYSBLSIZE        3
            SYSBSLR          0
            SYSBSLOFF        0
            SYSBSLPE         1
        SYSJMBC              0x000c
            JMBIN0FG         0
            JMBIN1FG         0
            JMBOUT0FG        1
            JMBOUT1FG        1
            JMBMODE          0
            JMBCLR0OFF       0
            JMBCLR1OFF       0
        SYSJMBI0             0x0110
        SYSJMBI1             0xffff
        SYSJMBO0             0x0000
        SYSJMBO1             0x0000
        SYSBERRIV            0x0000
        SYSUNIV              0x0000
            SYSUNVEC         0
        SYSSNIV              0x0000
            SYSNVEC          0
        SYSRSTIV             0x0000
            SYSRSTVEC        0
    I then brought the voltage back up to 3.3V and captured the registers:
    PMM
        PMMCTL0              0x9603
            PMMCOREV         3
            PMMSWBOR         0
            PMMSWPOR         0
            PMMSREGOFF       0
            PMMHPMRE         0
            PMMKEY           0x96
        PMMCTL1              0x0000
            PMMREFMD         0
            PMMREFACC        0
            PMMCMD           0x0
        SVSMHCTL             0x4707
            SVSMHRRL         0x7
            SVSMHDLYST       0
            SVSHMD           0
            SVSMHEVM         0
            SVSMHACE         0
            SVSHRVL          0x3
            SVSHE            1
            SVSHFP           0
            SVMHOVPE         0
            SVMHE            1
            SVMHFP           0
            SVSMLRRL         0x3
            SVSMLDLYST       0
            SVSLMD           0
            SVSMLEVM         0
            SVSMLACE         0
            SVSLRVL          0x3
            SVSLE            1
            SVSLFP           0
            SVMLOVPE         0
            SVMLE            1
            SVMLFP           0
        SVSMIO               0x0020
            SVSLEVE          0
            SVMLEVE          0
            SVMLOE           0
            SVMLVRLOE        0
            SVMOUTPOL        1
            SVSHEVE          0
            SVMHEVE          0
            SVMHOE           0
            SVMHVRLOE        0
        PMMIFG               0x0010
            SVSMLDLYIFG      0
            SVMLIFG          0
            SVMLVLRIFG       0
            SVSMHDLYIFG      1
            SVMHIFG          0
            SVMHVLRIFG       0
            PMMBORIFG        0
            PMMRSTIFG        0
            PMMPORIFG        0
            SVSHIFG          0
            SVSLIFG          0
            PMMRSTLPM5IFG    0
        PMMRIE               0x1146
            SVSMLDLYIE       0
            SVMLIE           1
            SVMLVLRIE        1
            SVSMHDLYIE       0
            SVMHIE           0
            SVMHVLRIE        1
            SVSLPE           1
            SVMLVLRPE        0
            SVSHPE           1
            SVMHVLRPE        0
        PM5CTL0              0x0000
            LOCKLPM5         0
    SYS
        SYSCTL               0x0000
            SYSRIVECT        0
            SYSPMMPE         0
            SYSBSLIND        0
            SYSJTAGPIN       0
        SYSBSLC              0x8003
            SYSBLSIZE        3
            SYSBSLR          0
            SYSBSLOFF        0
            SYSBSLPE         1
        SYSJMBC              0x000c
            JMBIN0FG         0
            JMBIN1FG         0
            JMBOUT0FG        1
            JMBOUT1FG        1
            JMBMODE          0
            JMBCLR0OFF       0
            JMBCLR1OFF       0
        SYSJMBI0             0x0110
        SYSJMBI1             0xffff
        SYSJMBO0             0x0000
        SYSJMBO1             0x0000
        SYSBERRIV            0x0000
        SYSUNIV              0x0000
            SYSUNVEC         0
        SYSSNIV              0x0000
            SYSNVEC          0
        SYSRSTIV             0x0000
            SYSRSTVEC        0
  • You need to re-enable the interrupt.
    When the SVMHIE interrupt vector is read it clears SVMIE ( fyi, same goes for SVMLIE ). Try re-enabling it in the VLRHIFG ISR case, also do this for SVMLIE in VLRLIFG.
    Another thing I noticed as that SVMHIFG is set it in SVMHIFG-regs-2, and stays set until regs-4. This may need to be investigated.
  • Thanks, it works now.