BQ76952: Autonomous Cell Balancing Test Failure on BQ76952 Evaluation Board

Part Number: BQ76952

Hello TI Team,

I am working on: 

BQ76952EVM

BMS029B

We are having issues with Testing Cell Balancing Feature on the Evaluation Board. I am sending a config file (.gg file) which is configured to measure 15 cell voltages, measuring 3 cell temperatures (using ports TS1, TS2 &TS3 pins configured as thermistor inputs to measure cell temperatures) and autonomously balance cells (Balance 15 cells at Maximum in parallel).

I checked all the parameters which can block Cell balancing as mentioned in the BQ76952 reference manual: 

None of these parameters/faults/protections/modes are triggered which can be verified with the log file attached below.

We tried Autonomous cell Balancing both in Normal as well as in Sleep mode and none of them gave me an indication on the Alarm status (CB signal - enabled if cell balancing is Active). We also verified by checking the 'Active cells Cell Balancing ' [0x0083 CB_ACTIVE_CELLS] subcommand which displays the address of cells being balanced. Also, can you inform me about any Gates that I can probe to check if Cell Balancing is active or not. We also tried host control cell balancing (writing 0x0083 CB_ACTIVE_CELLS() & 0x0084 CB_SET_LVL()) which responds in the same manner with no change while reading 'Active cells Cell Balancing ' [0x0083 CB_ACTIVE_CELLS] subcommand. It displays a zero value even after I write it with a specific cell address. Can anyone please verify my sequence and point out if you think I am doing a step incorrect?

* Texas Instruments Data Flash File				
* File created Wed Feb 14 18:24:37 2024				
*				
* Device Number 7695				
* Firmware Version 0.36				
* Build Number 39				
* Order Number 0				
*				
* bqz Device Number 7692				
* bqz Firmware Version 0.36				
* bqz Build Number 39				
*				
* Field Order: Class name	 Subclass name	 Parameter name	 Parameter Value	 Display Units
Calibration	Voltage	Cell 1 Gain	12119	—
Calibration	Voltage	Cell 2 Gain	12119	—
Calibration	Voltage	Cell 3 Gain	12119	—
Calibration	Voltage	Cell 4 Gain	12119	—
Calibration	Voltage	Cell 5 Gain	12119	—
Calibration	Voltage	Cell 6 Gain	12119	—
Calibration	Voltage	Cell 7 Gain	12119	—
Calibration	Voltage	Cell 8 Gain	12119	—
Calibration	Voltage	Cell 9 Gain	12119	—
Calibration	Voltage	Cell 10 Gain	12119	—
Calibration	Voltage	Cell 11 Gain	12119	—
Calibration	Voltage	Cell 12 Gain	12119	—
Calibration	Voltage	Cell 13 Gain	12119	—
Calibration	Voltage	Cell 14 Gain	12119	—
Calibration	Voltage	Cell 15 Gain	12119	—
Calibration	Voltage	Cell 16 Gain	12119	—
Calibration	Voltage	Pack Gain	34147	—
Calibration	Voltage	TOS Gain	34394	—
Calibration	Voltage	LD Gain	33871	—
Calibration	Voltage	ADC Gain	4038	—
Calibration	Current	CC Gain	10.011	mΩ
Calibration	Current	Capacity Gain	3.012	mΩ
Calibration	Vcell Offset	Vcell Offset	0	mV
Calibration	V Divider Offset	Vdiv Offset	0	userV
Calibration	Current Offset	Coulomb Counter Offset Samples	64	—
Calibration	Current Offset	Board Offset	0	—
Calibration	Temperature	Internal Temp Offset	0	°C
Calibration	Temperature	CFETOFF Temp Offset	0	°C
Calibration	Temperature	DFETOFF Temp Offset	0	°C
Calibration	Temperature	ALERT Temp Offset	0	°C
Calibration	Temperature	TS1 Temp Offset	0	°C
Calibration	Temperature	TS2 Temp Offset	0	°C
Calibration	Temperature	TS3 Temp Offset	0	°C
Calibration	Temperature	HDQ Temp Offset	0	°C
Calibration	Temperature	DCHG Temp Offset	0	°C
Calibration	Temperature	DDSG Temp Offset	0	°C
Calibration	Internal Temp Model	Int Gain	25390	—
Calibration	Internal Temp Model	Int base offset	3032	—
Calibration	Internal Temp Model	Int Maximum AD	16383	—
Calibration	Internal Temp Model	Int Maximum Temp	6379	0.1K
Calibration	18K Temperature Model	Coeff a1	-15524	—
Calibration	18K Temperature Model	Coeff a2	26423	—
Calibration	18K Temperature Model	Coeff a3	-22664	—
Calibration	18K Temperature Model	Coeff a4	28834	—
Calibration	18K Temperature Model	Coeff a5	672	—
Calibration	18K Temperature Model	Coeff b1	-371	—
Calibration	18K Temperature Model	Coeff b2	708	—
Calibration	18K Temperature Model	Coeff b3	-3498	—
Calibration	18K Temperature Model	Coeff b4	5051	—
Calibration	18K Temperature Model	Adc0	11703	—
Calibration	180K Temperature Model	Coeff a1	-17513	—
Calibration	180K Temperature Model	Coeff a2	25759	—
Calibration	180K Temperature Model	Coeff a3	-23593	—
Calibration	180K Temperature Model	Coeff a4	32175	—
Calibration	180K Temperature Model	Coeff a5	2090	—
Calibration	180K Temperature Model	Coeff b1	-2055	—
Calibration	180K Temperature Model	Coeff b2	2955	—
Calibration	180K Temperature Model	Coeff b3	-3427	—
Calibration	180K Temperature Model	Coeff b4	4385	—
Calibration	180K Temperature Model	Adc0	17246	—
Calibration	Custom Temperature Model	Coeff a1	0	—
Calibration	Custom Temperature Model	Coeff a2	0	—
Calibration	Custom Temperature Model	Coeff a3	0	—
Calibration	Custom Temperature Model	Coeff a4	0	—
Calibration	Custom Temperature Model	Coeff a5	0	—
Calibration	Custom Temperature Model	Coeff b1	0	—
Calibration	Custom Temperature Model	Coeff b2	0	—
Calibration	Custom Temperature Model	Coeff b3	0	—
Calibration	Custom Temperature Model	Coeff b4	0	—
Calibration	Custom Temperature Model	Rc0	0	—
Calibration	Custom Temperature Model	Adc0	0	—
Calibration	Current Deadband	Coulomb Counter Deadband	9	234nV
Calibration	CUV	CUV Threshold Override	ffff	Hex
Calibration	COV	COV Threshold Override	ffff	Hex
Settings	Fuse	Min Blow Fuse Voltage	5000	mV
Settings	Fuse	Fuse Blow Timeout	30	s
Settings	Configuration	Power Config	29b2	Hex
Settings	Configuration	REG12 Config	00	Hex
Settings	Configuration	REG0 Config	00	Hex
Settings	Configuration	HWD Regulator Options	00	Hex
Settings	Configuration	Comm Type	00	—
Settings	Configuration	I2C Address	00	—
Settings	Configuration	SPI Configuration	20	—
Settings	Configuration	Comm Idle Time	0	s
Settings	Configuration	CFETOFF Pin Config	00	Hex
Settings	Configuration	DFETOFF Pin Config	00	Hex
Settings	Configuration	ALERT Pin Config	00	Hex
Settings	Configuration	TS1 Config	07	Hex
Settings	Configuration	TS2 Config	07	Hex
Settings	Configuration	TS3 Config	07	Hex
Settings	Configuration	HDQ Pin Config	00	Hex
Settings	Configuration	DCHG Pin Config	00	Hex
Settings	Configuration	DDSG Pin Config	00	Hex
Settings	Configuration	DA Configuration	05	Hex
Settings	Configuration	Vcell Mode	4000	Hex
Settings	Configuration	CC3 Samples	80	Num
Settings	Protection	Protection Configuration	0002	Hex
Settings	Protection	Enabled Protections A	88	Hex
Settings	Protection	Enabled Protections B	00	Hex
Settings	Protection	Enabled Protections C	00	Hex
Settings	Protection	CHG FET Protections A	98	Hex
Settings	Protection	CHG FET Protections B	d5	Hex
Settings	Protection	CHG FET Protections C	56	Hex
Settings	Protection	DSG FET Protections A	e4	Hex
Settings	Protection	DSG FET Protections B	e6	Hex
Settings	Protection	DSG FET Protections C	e2	Hex
Settings	Protection	Body Diode Threshold	50	mA
Settings	Alarm	Default Alarm Mask	f887	Hex
Settings	Alarm	SF Alert Mask A	fc	Hex
Settings	Alarm	SF Alert Mask B	f7	Hex
Settings	Alarm	SF Alert Mask C	f4	Hex
Settings	Alarm	PF Alert Mask A	5f	Hex
Settings	Alarm	PF Alert Mask B	9f	Hex
Settings	Alarm	PF Alert Mask C	00	Hex
Settings	Alarm	PF Alert Mask D	00	Hex
Settings	Permanent Failure	Enabled PF A	00	Hex
Settings	Permanent Failure	Enabled PF B	00	Hex
Settings	Permanent Failure	Enabled PF C	07	Hex
Settings	Permanent Failure	Enabled PF D	00	Hex
Settings	FET	FET Options	0f	Hex
Settings	FET	Chg Pump Control	01	Hex
Settings	FET	Precharge Start Voltage	0	mV
Settings	FET	Precharge Stop Voltage	0	mV
Settings	FET	Predischarge Timeout	5	10ms
Settings	FET	Predischarge Stop Delta	500	mV
Settings	Current Thresholds	Dsg Current Threshold	10	userA
Settings	Current Thresholds	Chg Current Threshold	10	userA
Settings	Cell Open-Wire	Check Time	5	s
Settings	Interconnect Resistances	Cell 1 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 2 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 3 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 4 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 5 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 6 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 7 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 8 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 9 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 10 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 11 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 12 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 13 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 14 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 15 Interconnect	0	mΩ
Settings	Interconnect Resistances	Cell 16 Interconnect	0	mΩ
Settings	Manufacturing	Mfg Status Init	0050	Hex
Settings	Cell Balancing Config	Balancing Configuration	17	Hex
Settings	Cell Balancing Config	Min Cell Temp	-20	°C
Settings	Cell Balancing Config	Max Cell Temp	60	°C
Settings	Cell Balancing Config	Max Internal Temp	70	°C
Settings	Cell Balancing Config	Cell Balance Interval	20	s
Settings	Cell Balancing Config	Cell Balance Max Cells	15	Num
Settings	Cell Balancing Config	Cell Balance Min Cell V (Charge)	3000	mV
Settings	Cell Balancing Config	Cell Balance Min Delta (Charge)	30	mV
Settings	Cell Balancing Config	Cell Balance Stop Delta (Charge)	5	mV
Settings	Cell Balancing Config	Cell Balance Min Cell V (Relax)	3000	mV
Settings	Cell Balancing Config	Cell Balance Min Delta (Relax)	30	mV
Settings	Cell Balancing Config	Cell Balance Stop Delta (Relax)	5	mV
Power	Shutdown	Shutdown Cell Voltage	0	mV
Power	Shutdown	Shutdown Stack Voltage	6000	mV
Power	Shutdown	Low V Shutdown Delay	1	s
Power	Shutdown	Shutdown Temperature	85	°C
Power	Shutdown	Shutdown Temperature Delay	5	s
Power	Shutdown	FET Off Delay	0	0.25s
Power	Shutdown	Shutdown Command Delay	0	0.25s
Power	Shutdown	Auto Shutdown Time	0	min
Power	Shutdown	RAM Fail Shutdown Time	5	s
Power	Sleep	Sleep Current	20	mA
Power	Sleep	Voltage Time	5	s
Power	Sleep	Wake Comparator Current	500	mA
Power	Sleep	Sleep Hysteresis Time	10	s
Power	Sleep	Sleep Charger Voltage Threshold	20000	mV
Power	Sleep	Sleep Charger PACK-TOS Delta	2000	mV
System Data	Integrity	Config RAM Signature	0000	Hex
Protections	CUV	Threshold	50	50.6mV
Protections	CUV	Delay	74	3.3 ms
Protections	CUV	Recovery Hysteresis	2	50.6mV
Protections	COV	Threshold	86	50.6mV
Protections	COV	Delay	74	3.3 ms
Protections	COV	Recovery Hysteresis	2	50.6mV
Protections	COVL	Latch Limit	0	—
Protections	COVL	Counter Dec Delay	10	s
Protections	COVL	Recovery Time	15	s
Protections	OCC	Threshold	4	mV
Protections	OCC	Delay	4	3.3 ms
Protections	OCC	Recovery Threshold	-200	mA
Protections	OCC	PACK-TOS Delta	2000	mV
Protections	OCD1	Threshold	8	mV
Protections	OCD1	Delay	1	3.3 ms
Protections	OCD2	Threshold	6	mV
Protections	OCD2	Delay	7	3.3 ms
Protections	SCD	Threshold	0	—
Protections	SCD	Delay	15	µs
Protections	SCD	Recovery Time	5	s
Protections	OCD3	Threshold	-4000	userA
Protections	OCD3	Delay	2	s
Protections	OCD	Recovery Threshold	200	mA
Protections	OCDL	Latch Limit	0	—
Protections	OCDL	Counter Dec Delay	10	s
Protections	OCDL	Recovery Time	15	s
Protections	OCDL	Recovery Threshold	200	mA
Protections	SCDL	Latch Limit	0	—
Protections	SCDL	Counter Dec Delay	10	s
Protections	SCDL	Recovery Time	15	s
Protections	SCDL	Recovery Threshold	200	mA
Protections	OTC	Threshold	55	°C
Protections	OTC	Delay	2	s
Protections	OTC	Recovery	50	°C
Protections	OTD	Threshold	60	°C
Protections	OTD	Delay	2	s
Protections	OTD	Recovery	55	°C
Protections	OTF	Threshold	80	°C
Protections	OTF	Delay	2	s
Protections	OTF	Recovery	65	°C
Protections	OTINT	Threshold	85	°C
Protections	OTINT	Delay	2	s
Protections	OTINT	Recovery	80	°C
Protections	UTC	Threshold	0	°C
Protections	UTC	Delay	2	s
Protections	UTC	Recovery	5	°C
Protections	UTD	Threshold	0	°C
Protections	UTD	Delay	2	s
Protections	UTD	Recovery	5	°C
Protections	UTINT	Threshold	-20	°C
Protections	UTINT	Delay	2	s
Protections	UTINT	Recovery	-15	°C
Protections	Recovery	Time	3	s
Protections	HWD	Delay	60	s
Protections	Load Detect	Active Time	0	s
Protections	Load Detect	Retry Delay	50	s
Protections	Load Detect	Timeout	1	hrs
Protections	PTO	Charge Threshold	250	mA
Protections	PTO	Delay	1800	s
Protections	PTO	Reset	2	userAh
Permanent Fail	CUDEP	Threshold	1500	mV
Permanent Fail	CUDEP	Delay	2	s
Permanent Fail	SUV	Threshold	2200	mV
Permanent Fail	SUV	Delay	5	s
Permanent Fail	SOV	Threshold	4500	mV
Permanent Fail	SOV	Delay	5	s
Permanent Fail	TOS	Threshold	500	mV
Permanent Fail	TOS	Delay	5	s
Permanent Fail	SOCC	Threshold	10000	userA
Permanent Fail	SOCC	Delay	5	s
Permanent Fail	SOCD	Threshold	-32000	userA
Permanent Fail	SOCD	Delay	5	s
Permanent Fail	SOT	Threshold	65	°C
Permanent Fail	SOT	Delay	5	s
Permanent Fail	SOTF	Threshold	85	°C
Permanent Fail	SOTF	Delay	5	s
Permanent Fail	VIMR	Check Voltage	3500	mV
Permanent Fail	VIMR	Max Relax Current	10	mA
Permanent Fail	VIMR	Threshold	500	mV
Permanent Fail	VIMR	Delay	5	s
Permanent Fail	VIMR	Relax Min Duration	100	s
Permanent Fail	VIMA	Check Voltage	3700	mV
Permanent Fail	VIMA	Min Active Current	50	mA
Permanent Fail	VIMA	Threshold	200	mV
Permanent Fail	VIMA	Delay	5	s
Permanent Fail	CFETF	OFF Threshold	20	mA
Permanent Fail	CFETF	OFF Delay	5	s
Permanent Fail	DFETF	OFF Threshold	-20	mA
Permanent Fail	DFETF	OFF Delay	5	s
Permanent Fail	VSSF	Fail Threshold	100	—
Permanent Fail	VSSF	Delay	5	s
Permanent Fail	2LVL	Delay	5	s
Permanent Fail	LFOF	Delay	5	s
Permanent Fail	HWMX	Delay	5	s
Security	Settings	Security Settings	00	Hex
Security	Keys	Unseal Key Step 1	0414	Hex
Security	Keys	Unseal Key Step 2	3672	Hex
Security	Keys	Full Access Key Step 1	ffff	Hex
Security	Keys	Full Access Key Step 2	ffff	Hex

For Specifics, here is the snippet of my Cell Balancing configuration and all the parameters associated with it: 

I am also attaching a log file which gives no indication of the cell balancing statuses.

Wed Feb 14 18:29:52 EST 2024

Device Version Info = 7695_0_36
BQZ Device Name = bq76952
BQZ Firmware Version = 0_36


Sample,DateTime,ElapsedTime,ControlStatus,SafetyAlertA,SafetyStatusA,SafetyAlertB,SafetyStatusB,SafetyAlertC,SafetyStatusC,PFAlertA,PFStatusA,PFAlertB,PFStatusB,PFAlertC,PFStatusC,PFAlertD,PFStatusD,BatteryStatus,Cell1Voltage,Cell2Voltage,Cell3Voltage,Cell4Voltage,Cell5Voltage,Cell6Voltage,Cell7Voltage,Cell8Voltage,Cell9Voltage,Cell10Voltage,Cell11Voltage,Cell12Voltage,Cell13Voltage,Cell14Voltage,Cell15Voltage,Cell16Voltage,StackVoltage,PACKPinVoltage,LDPinVoltage,CC2Current,AlarmStatus,AlarmRawStatus,AlarmEnable,IntTemperature,CFETOFFTemperature,DFETOFFTemperature,ALERTTemperature,TS1Temperature,TS2Temperature,TS3Temperature,HDQTemperature,DCHGTemperature,DDSGTemperature,FETStatus,ManufacturingStatus,CellTemperature,FETTemperature,CC3Current,CC1Current,AccumCharge,AccumTime,CellBalancingActiveCells,CellBalancingPresentTime,LogRowTime(ms),LogStatus
1,2024-02-14 18:29:57,5.011,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3877,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5217,5136,5159,2,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.5,24.6,20.6,-59.5,-59.7,-59.7,0x45,0x0050,21.9,-273.2,0,2,13,18997,0x0000,0,1168,SUCCESS
2,2024-02-14 18:30:02,10.020,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3877,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5216,5135,5158,-1,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.5,24.6,20.6,-59.5,-59.7,-59.7,0x45,0x0050,21.9,-273.2,0,-1,13,19002,0x0000,0,1006,SUCCESS
3,2024-02-14 18:30:07,15.033,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3877,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5216,5135,5159,0,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.5,24.7,20.6,-59.5,-59.7,-59.7,0x45,0x0050,21.9,-273.2,0,0,13,19007,0x0000,0,1020,SUCCESS
4,2024-02-14 18:30:12,20.037,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3877,3338,3518,3601,3330,3808,3330,3785,3670,0,3403,5217,5135,5159,-2,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.5,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-2,13,19012,0x0000,0,1017,SUCCESS
5,2024-02-14 18:30:17,25.047,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3877,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5217,5136,5160,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19017,0x0000,0,1002,SUCCESS
6,2024-02-14 18:30:22,30.063,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5216,5136,5159,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19022,0x0000,0,1116,SUCCESS
7,2024-02-14 18:30:28,35.075,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5217,5135,5160,0,0x0083,0x0682,0xF887,21.0,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19027,0x0000,0,1042,SUCCESS
8,2024-02-14 18:30:33,40.075,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3785,3670,0,3402,5216,5135,5160,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19032,0x0000,0,1384,SUCCESS
9,2024-02-14 18:30:38,45.092,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5217,5136,5158,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19038,0x0000,0,2380,SUCCESS
10,2024-02-14 18:30:43,50.101,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5216,5135,5158,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19043,0x0000,0,2416,SUCCESS
11,2024-02-14 18:30:48,55.107,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5217,5135,5158,-1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19048,0x0000,0,2250,SUCCESS
12,2024-02-14 18:30:53,60.114,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5216,5136,5160,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19053,0x0000,0,2228,SUCCESS
13,2024-02-14 18:30:58,65.121,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5216,5136,5160,0,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19058,0x0000,0,2146,SUCCESS
14,2024-02-14 18:31:03,70.126,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5216,5135,5159,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19063,0x0000,0,2132,SUCCESS
15,2024-02-14 18:31:08,75.134,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3784,3669,0,3402,5216,5135,5158,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19068,0x0000,0,2110,SUCCESS
16,2024-02-14 18:31:13,80.138,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5216,5135,5161,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19073,0x0000,0,2268,SUCCESS
17,2024-02-14 18:31:18,85.145,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3784,3669,0,3402,5216,5135,5161,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19078,0x0000,0,2270,SUCCESS
18,2024-02-14 18:31:23,90.152,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3876,3339,3517,3601,3330,3807,3330,3784,3668,0,3402,5216,5135,5159,-1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19083,0x0000,0,2321,SUCCESS
19,2024-02-14 18:31:28,95.162,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3876,3338,3517,3601,3330,3807,3330,3784,3668,0,3402,5216,5135,5159,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19088,0x0000,0,2335,SUCCESS
20,2024-02-14 18:31:33,100.165,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3517,3601,3330,3807,3330,3784,3668,0,3402,5215,5136,5158,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19093,0x0000,0,2182,SUCCESS
21,2024-02-14 18:31:38,105.166,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3876,3338,3517,3601,3330,3807,3330,3784,3668,0,3401,5216,5135,5159,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19098,0x0000,0,2343,SUCCESS
22,2024-02-14 18:31:43,110.169,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3875,3338,3517,3601,3330,3807,3330,3784,3668,0,3401,5217,5135,5158,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19103,0x0000,0,2223,SUCCESS
23,2024-02-14 18:31:48,115.183,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3784,3668,0,3401,5216,5135,5158,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19108,0x0000,0,2212,SUCCESS
24,2024-02-14 18:31:53,120.195,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3784,3668,0,3401,5216,5135,5157,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19113,0x0000,0,2294,SUCCESS
25,2024-02-14 18:31:58,125.198,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3875,3338,3516,3601,3330,3807,3330,3784,3668,0,3401,5215,5135,5158,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19118,0x0000,0,2176,SUCCESS
26,2024-02-14 18:32:03,130.206,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3784,3668,0,3401,5216,5134,5158,0,0x0083,0x0682,0xF887,20.5,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19123,0x0000,0,2249,SUCCESS
27,2024-02-14 18:32:08,135.217,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3784,3668,0,3401,5217,5135,5158,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19128,0x0000,0,2270,SUCCESS
28,2024-02-14 18:32:13,140.236,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3783,3668,0,3401,5215,5135,5158,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19134,0x0000,0,2876,SUCCESS
29,2024-02-14 18:32:18,145.237,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3875,3338,3516,3601,3330,3807,3330,3783,3668,0,3401,5215,5135,5158,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19138,0x0000,0,2224,SUCCESS
30,2024-02-14 18:32:23,150.246,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3784,3667,0,3401,5216,5135,5159,0,0x0083,0x0682,0xF887,20.5,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19143,0x0000,0,2211,SUCCESS
31,2024-02-14 18:32:28,155.251,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3783,3667,0,3401,5216,5135,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19148,0x0000,0,2294,SUCCESS
32,2024-02-14 18:32:33,160.258,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3783,3667,0,3401,5216,5135,5158,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19153,0x0000,0,2128,SUCCESS
33,2024-02-14 18:32:38,165.260,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3783,3667,0,3401,5216,5134,5158,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19158,0x0000,0,2067,SUCCESS
34,2024-02-14 18:32:43,170.264,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3516,3601,3330,3806,3330,3783,3667,0,3401,5215,5134,5158,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19163,0x0000,0,2269,SUCCESS
35,2024-02-14 18:32:48,175.271,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3516,3601,3330,3806,3330,3783,3667,0,3401,5215,5135,5157,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19168,0x0000,0,2114,SUCCESS
36,2024-02-14 18:32:53,180.275,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3339,3516,3601,3330,3806,3330,3783,3667,0,3401,5215,5135,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19173,0x0000,0,2176,SUCCESS
37,2024-02-14 18:32:58,185.288,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3806,3330,3783,3667,0,3401,5215,5134,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19178,0x0000,0,2214,SUCCESS
38,2024-02-14 18:33:03,190.294,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3339,3516,3601,3330,3806,3330,3783,3667,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19183,0x0000,0,2256,SUCCESS
39,2024-02-14 18:33:08,195.303,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3516,3601,3330,3806,3330,3783,3666,0,3401,5216,5134,5157,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19188,0x0000,0,2186,SUCCESS
40,2024-02-14 18:33:13,200.310,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3516,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19193,0x0000,0,2240,SUCCESS
41,2024-02-14 18:33:18,205.313,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3874,3339,3516,3601,3330,3806,3330,3783,3666,0,3400,5216,5134,5158,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19198,0x0000,0,2300,SUCCESS
42,2024-02-14 18:33:23,210.315,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3516,3600,3330,3806,3330,3783,3666,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19203,0x0000,0,2347,SUCCESS
43,2024-02-14 18:33:28,215.325,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3516,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5158,2,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19208,0x0000,0,2132,SUCCESS
44,2024-02-14 18:33:33,220.330,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3874,3338,3515,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5158,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19213,0x0000,0,2388,SUCCESS
45,2024-02-14 18:33:38,225.345,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3515,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5157,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19218,0x0000,0,2307,SUCCESS
46,2024-02-14 18:33:43,230.358,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3874,3338,3516,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5157,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19223,0x0000,0,2077,SUCCESS
47,2024-02-14 18:33:48,235.379,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3874,3338,3516,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19228,0x0000,0,2257,SUCCESS
48,2024-02-14 18:33:53,240.385,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3874,3338,3515,3601,3330,3806,3330,3782,3666,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19237,0x0000,0,5650,SUCCESS
49,2024-02-14 18:33:59,246.641,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3874,3338,3516,3601,3330,3806,3330,3782,3666,0,3400,5214,5134,5157,0,0x0083,0x0682,0xF887,20.5,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19243,0x0000,0,5352,SUCCESS
50,2024-02-14 18:34:05,252.626,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3400,5214,5134,5157,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19246,0x0000,0,2168,SUCCESS
51,2024-02-14 18:34:08,255.781,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3874,3338,3515,3601,3330,3806,3330,3782,3665,0,3399,5216,5134,5157,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19249,0x0000,0,2277,SUCCESS
52,2024-02-14 18:34:13,260.782,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3399,5216,5134,5157,-1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19254,0x0000,0,2215,SUCCESS
53,2024-02-14 18:34:18,265.998,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3874,3338,3515,3601,3330,3806,3330,3782,3665,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19259,0x0000,0,2255,SUCCESS
54,2024-02-14 18:34:23,270.806,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3400,5214,5134,5156,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19264,0x0000,0,2264,SUCCESS
55,2024-02-14 18:34:28,275.812,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3400,5214,5133,5158,2,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,2,13,19269,0x0000,0,2292,SUCCESS
56,2024-02-14 18:34:33,280.818,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3399,5214,5134,5157,-1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19274,0x0000,0,2174,SUCCESS
57,2024-02-14 18:34:38,285.997,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3665,0,3399,5214,5134,5158,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19280,0x0000,0,3326,SUCCESS
58,2024-02-14 18:34:44,291.077,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3399,5215,5134,5157,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19284,0x0000,0,2486,SUCCESS
59,2024-02-14 18:34:49,296.085,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5214,5133,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19289,0x0000,0,2392,SUCCESS
60,2024-02-14 18:34:54,301.086,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5215,5134,5156,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19294,0x0000,0,2355,SUCCESS
61,2024-02-14 18:34:59,306.086,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5216,5133,5158,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19299,0x0000,0,2345,SUCCESS
62,2024-02-14 18:35:04,311.090,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5215,5133,5157,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19304,0x0000,0,2367,SUCCESS
63,2024-02-14 18:35:09,316.102,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5215,5133,5157,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19309,0x0000,0,2229,SUCCESS
64,2024-02-14 18:35:14,321.114,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5215,5133,5156,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19314,0x0000,0,2353,SUCCESS
65,2024-02-14 18:35:19,326.130,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5214,5134,5157,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19319,0x0000,0,2305,SUCCESS
66,2024-02-14 18:35:24,331.266,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3781,3664,0,3399,5213,5133,5156,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19324,0x0000,0,2180,SUCCESS
67,2024-02-14 18:35:29,336.443,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3398,5213,5134,5157,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19331,0x0000,0,3333,SUCCESS
68,2024-02-14 18:35:34,341.516,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3781,3663,0,3398,5214,5134,5157,2,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,2,13,19336,0x0000,0,3383,SUCCESS
69,2024-02-14 18:35:39,346.998,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3873,3338,3514,3601,3330,3805,3330,3781,3664,0,3399,5214,5134,5156,-1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19343,0x0000,0,4884,SUCCESS
70,2024-02-14 18:35:45,352.453,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3781,3663,0,3399,5215,5133,5157,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19347,0x0000,0,3348,SUCCESS
71,2024-02-14 18:35:49,357.062,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3514,3601,3330,3805,3330,3781,3663,0,3398,5215,5134,5158,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19350,0x0000,0,2399,SUCCESS
72,2024-02-14 18:35:54,361.390,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5213,5133,5157,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19355,0x0000,0,2506,SUCCESS
73,2024-02-14 18:35:59,366.742,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3515,3601,3330,3805,3330,3781,3663,0,3398,5213,5133,5156,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19362,0x0000,0,4620,SUCCESS
74,2024-02-14 18:36:05,372.096,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5215,5134,5157,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19366,0x0000,0,2825,SUCCESS
75,2024-02-14 18:36:09,376.420,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5214,5133,5157,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19370,0x0000,0,2326,SUCCESS
76,2024-02-14 18:36:14,381.432,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3873,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5213,5133,5157,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19375,0x0000,0,2192,SUCCESS
77,2024-02-14 18:36:19,386.559,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5213,5133,5156,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19380,0x0000,0,2993,SUCCESS
78,2024-02-14 18:36:24,391.496,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5214,5133,5157,-1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19385,0x0000,0,2307,SUCCESS
79,2024-02-14 18:36:29,396.486,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3872,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5213,5133,5156,-2,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-2,13,19390,0x0000,0,2280,SUCCESS
80,2024-02-14 18:36:34,401.491,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5214,5133,5157,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19395,0x0000,0,2201,SUCCESS
81,2024-02-14 18:36:39,406.603,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3662,0,3398,5213,5133,5157,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19400,0x0000,0,2248,SUCCESS
82,2024-02-14 18:36:44,411.508,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3872,3338,3514,3601,3330,3804,3330,3781,3662,0,3398,5213,5133,5156,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19405,0x0000,0,2227,SUCCESS
83,2024-02-14 18:36:49,416.521,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3662,0,3398,5214,5133,5156,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19410,0x0000,0,2235,SUCCESS
84,2024-02-14 18:36:54,421.527,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3780,3662,0,3398,5213,5133,5156,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19415,0x0000,0,2255,SUCCESS
85,2024-02-14 18:36:59,426.615,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3780,3662,0,3397,5213,5133,5156,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19420,0x0000,0,2393,SUCCESS
86,2024-02-14 18:37:04,431.545,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3662,0,3397,5213,5133,5155,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19425,0x0000,0,2635,SUCCESS
87,2024-02-14 18:37:09,436.547,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3872,3338,3514,3601,3330,3804,3330,3781,3662,0,3397,5213,5133,5157,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19430,0x0000,0,2564,SUCCESS
88,2024-02-14 18:37:14,441.553,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3872,3338,3514,3601,3330,3804,3330,3780,3662,0,3397,5213,5132,5157,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19435,0x0000,0,2569,SUCCESS
89,2024-02-14 18:37:19,446.727,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3780,3662,0,3397,5212,5133,5156,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19440,0x0000,0,2302,SUCCESS
90,2024-02-14 18:37:24,451.565,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3513,3601,3330,3803,3330,3780,3661,0,3397,5213,5132,5157,-1,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19445,0x0000,0,2289,SUCCESS
91,2024-02-14 18:37:29,456.569,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3514,3601,3330,3803,3330,3780,3661,1,3397,5213,5132,5156,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19450,0x0000,0,2212,SUCCESS
92,2024-02-14 18:37:34,461.572,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3872,3338,3514,3601,3330,3803,3330,3780,3661,0,3397,5213,5133,5156,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19455,0x0000,0,2301,SUCCESS
93,2024-02-14 18:37:39,466.744,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3513,3601,3330,3803,3330,3780,3661,0,3397,5213,5132,5156,0,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19460,0x0000,0,2208,SUCCESS
94,2024-02-14 18:37:44,471.573,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3513,3601,3330,3803,3330,3780,3661,0,3397,5213,5133,5156,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19465,0x0000,0,2205,SUCCESS
95,2024-02-14 18:37:49,476.583,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3872,3338,3513,3601,3330,3803,3330,3780,3661,0,3397,5212,5132,5156,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19470,0x0000,0,2215,SUCCESS
96,2024-02-14 18:37:54,481.593,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3872,3338,3513,3601,3330,3803,3330,3780,3661,0,3397,5213,5132,5156,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19475,0x0000,0,2272,SUCCESS
97,2024-02-14 18:37:59,486.752,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3871,3339,3513,3601,3330,3803,3330,3780,3661,0,3397,5213,5132,5156,-1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19480,0x0000,0,2050,SUCCESS

Thank you.

Awaiting in Anticipation.

  • Hello,

    Did you configure the cell balancing as detailed in Section 3 Stand-Alone Balancing Algorithm and Settings of the Cell Balancing With BQ769x2 Battery Monitors application note?

    Mind uploading the log file as a separate file (Insert>Image/video/file), I would like to open it on excel to better understand the log.

    You can use CB_ACTIVE_CELLS() to see which cells are being balanced, if you want to see it externally, you'd need to use an oscilloscope probe on the pins directly, the cell balancing would look like Figure 2-3 of the application note mentioned above.

    Best Regards,

    Luis Hernandez Salomon

  • Wed Feb 14 18:29:52 EST 2024
    
    Device Version Info = 7695_0_36
    BQZ Device Name = bq76952
    BQZ Firmware Version = 0_36
    
    
    Sample,DateTime,ElapsedTime,ControlStatus,SafetyAlertA,SafetyStatusA,SafetyAlertB,SafetyStatusB,SafetyAlertC,SafetyStatusC,PFAlertA,PFStatusA,PFAlertB,PFStatusB,PFAlertC,PFStatusC,PFAlertD,PFStatusD,BatteryStatus,Cell1Voltage,Cell2Voltage,Cell3Voltage,Cell4Voltage,Cell5Voltage,Cell6Voltage,Cell7Voltage,Cell8Voltage,Cell9Voltage,Cell10Voltage,Cell11Voltage,Cell12Voltage,Cell13Voltage,Cell14Voltage,Cell15Voltage,Cell16Voltage,StackVoltage,PACKPinVoltage,LDPinVoltage,CC2Current,AlarmStatus,AlarmRawStatus,AlarmEnable,IntTemperature,CFETOFFTemperature,DFETOFFTemperature,ALERTTemperature,TS1Temperature,TS2Temperature,TS3Temperature,HDQTemperature,DCHGTemperature,DDSGTemperature,FETStatus,ManufacturingStatus,CellTemperature,FETTemperature,CC3Current,CC1Current,AccumCharge,AccumTime,CellBalancingActiveCells,CellBalancingPresentTime,LogRowTime(ms),LogStatus
    1,2024-02-14 18:29:57,5.011,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3877,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5217,5136,5159,2,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.5,24.6,20.6,-59.5,-59.7,-59.7,0x45,0x0050,21.9,-273.2,0,2,13,18997,0x0000,0,1168,SUCCESS
    2,2024-02-14 18:30:02,10.020,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3877,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5216,5135,5158,-1,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.5,24.6,20.6,-59.5,-59.7,-59.7,0x45,0x0050,21.9,-273.2,0,-1,13,19002,0x0000,0,1006,SUCCESS
    3,2024-02-14 18:30:07,15.033,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3877,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5216,5135,5159,0,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.5,24.7,20.6,-59.5,-59.7,-59.7,0x45,0x0050,21.9,-273.2,0,0,13,19007,0x0000,0,1020,SUCCESS
    4,2024-02-14 18:30:12,20.037,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3877,3338,3518,3601,3330,3808,3330,3785,3670,0,3403,5217,5135,5159,-2,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.5,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-2,13,19012,0x0000,0,1017,SUCCESS
    5,2024-02-14 18:30:17,25.047,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3877,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5217,5136,5160,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19017,0x0000,0,1002,SUCCESS
    6,2024-02-14 18:30:22,30.063,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5216,5136,5159,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19022,0x0000,0,1116,SUCCESS
    7,2024-02-14 18:30:28,35.075,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3785,3670,0,3403,5217,5135,5160,0,0x0083,0x0682,0xF887,21.0,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19027,0x0000,0,1042,SUCCESS
    8,2024-02-14 18:30:33,40.075,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3785,3670,0,3402,5216,5135,5160,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19032,0x0000,0,1384,SUCCESS
    9,2024-02-14 18:30:38,45.092,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5217,5136,5158,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19038,0x0000,0,2380,SUCCESS
    10,2024-02-14 18:30:43,50.101,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5216,5135,5158,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19043,0x0000,0,2416,SUCCESS
    11,2024-02-14 18:30:48,55.107,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5217,5135,5158,-1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19048,0x0000,0,2250,SUCCESS
    12,2024-02-14 18:30:53,60.114,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5216,5136,5160,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19053,0x0000,0,2228,SUCCESS
    13,2024-02-14 18:30:58,65.121,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5216,5136,5160,0,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19058,0x0000,0,2146,SUCCESS
    14,2024-02-14 18:31:03,70.126,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5216,5135,5159,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19063,0x0000,0,2132,SUCCESS
    15,2024-02-14 18:31:08,75.134,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3784,3669,0,3402,5216,5135,5158,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19068,0x0000,0,2110,SUCCESS
    16,2024-02-14 18:31:13,80.138,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3876,3338,3517,3601,3330,3808,3330,3785,3669,0,3402,5216,5135,5161,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19073,0x0000,0,2268,SUCCESS
    17,2024-02-14 18:31:18,85.145,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3876,3338,3517,3601,3330,3808,3330,3784,3669,0,3402,5216,5135,5161,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19078,0x0000,0,2270,SUCCESS
    18,2024-02-14 18:31:23,90.152,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3876,3339,3517,3601,3330,3807,3330,3784,3668,0,3402,5216,5135,5159,-1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19083,0x0000,0,2321,SUCCESS
    19,2024-02-14 18:31:28,95.162,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3876,3338,3517,3601,3330,3807,3330,3784,3668,0,3402,5216,5135,5159,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19088,0x0000,0,2335,SUCCESS
    20,2024-02-14 18:31:33,100.165,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3517,3601,3330,3807,3330,3784,3668,0,3402,5215,5136,5158,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19093,0x0000,0,2182,SUCCESS
    21,2024-02-14 18:31:38,105.166,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3876,3338,3517,3601,3330,3807,3330,3784,3668,0,3401,5216,5135,5159,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19098,0x0000,0,2343,SUCCESS
    22,2024-02-14 18:31:43,110.169,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3875,3338,3517,3601,3330,3807,3330,3784,3668,0,3401,5217,5135,5158,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19103,0x0000,0,2223,SUCCESS
    23,2024-02-14 18:31:48,115.183,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3784,3668,0,3401,5216,5135,5158,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19108,0x0000,0,2212,SUCCESS
    24,2024-02-14 18:31:53,120.195,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3784,3668,0,3401,5216,5135,5157,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19113,0x0000,0,2294,SUCCESS
    25,2024-02-14 18:31:58,125.198,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3875,3338,3516,3601,3330,3807,3330,3784,3668,0,3401,5215,5135,5158,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19118,0x0000,0,2176,SUCCESS
    26,2024-02-14 18:32:03,130.206,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3784,3668,0,3401,5216,5134,5158,0,0x0083,0x0682,0xF887,20.5,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19123,0x0000,0,2249,SUCCESS
    27,2024-02-14 18:32:08,135.217,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3784,3668,0,3401,5217,5135,5158,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19128,0x0000,0,2270,SUCCESS
    28,2024-02-14 18:32:13,140.236,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3783,3668,0,3401,5215,5135,5158,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19134,0x0000,0,2876,SUCCESS
    29,2024-02-14 18:32:18,145.237,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3875,3338,3516,3601,3330,3807,3330,3783,3668,0,3401,5215,5135,5158,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19138,0x0000,0,2224,SUCCESS
    30,2024-02-14 18:32:23,150.246,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3784,3667,0,3401,5216,5135,5159,0,0x0083,0x0682,0xF887,20.5,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19143,0x0000,0,2211,SUCCESS
    31,2024-02-14 18:32:28,155.251,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3783,3667,0,3401,5216,5135,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19148,0x0000,0,2294,SUCCESS
    32,2024-02-14 18:32:33,160.258,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3783,3667,0,3401,5216,5135,5158,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19153,0x0000,0,2128,SUCCESS
    33,2024-02-14 18:32:38,165.260,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3807,3330,3783,3667,0,3401,5216,5134,5158,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19158,0x0000,0,2067,SUCCESS
    34,2024-02-14 18:32:43,170.264,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3516,3601,3330,3806,3330,3783,3667,0,3401,5215,5134,5158,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19163,0x0000,0,2269,SUCCESS
    35,2024-02-14 18:32:48,175.271,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3338,3516,3601,3330,3806,3330,3783,3667,0,3401,5215,5135,5157,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19168,0x0000,0,2114,SUCCESS
    36,2024-02-14 18:32:53,180.275,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3875,3339,3516,3601,3330,3806,3330,3783,3667,0,3401,5215,5135,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19173,0x0000,0,2176,SUCCESS
    37,2024-02-14 18:32:58,185.288,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3875,3338,3516,3601,3330,3806,3330,3783,3667,0,3401,5215,5134,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19178,0x0000,0,2214,SUCCESS
    38,2024-02-14 18:33:03,190.294,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3339,3516,3601,3330,3806,3330,3783,3667,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19183,0x0000,0,2256,SUCCESS
    39,2024-02-14 18:33:08,195.303,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3516,3601,3330,3806,3330,3783,3666,0,3401,5216,5134,5157,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19188,0x0000,0,2186,SUCCESS
    40,2024-02-14 18:33:13,200.310,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3516,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19193,0x0000,0,2240,SUCCESS
    41,2024-02-14 18:33:18,205.313,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3874,3339,3516,3601,3330,3806,3330,3783,3666,0,3400,5216,5134,5158,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19198,0x0000,0,2300,SUCCESS
    42,2024-02-14 18:33:23,210.315,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3516,3600,3330,3806,3330,3783,3666,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19203,0x0000,0,2347,SUCCESS
    43,2024-02-14 18:33:28,215.325,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3516,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5158,2,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19208,0x0000,0,2132,SUCCESS
    44,2024-02-14 18:33:33,220.330,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3874,3338,3515,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5158,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19213,0x0000,0,2388,SUCCESS
    45,2024-02-14 18:33:38,225.345,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3515,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5157,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19218,0x0000,0,2307,SUCCESS
    46,2024-02-14 18:33:43,230.358,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3874,3338,3516,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5157,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19223,0x0000,0,2077,SUCCESS
    47,2024-02-14 18:33:48,235.379,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3874,3338,3516,3601,3330,3806,3330,3783,3666,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19228,0x0000,0,2257,SUCCESS
    48,2024-02-14 18:33:53,240.385,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3874,3338,3515,3601,3330,3806,3330,3782,3666,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19237,0x0000,0,5650,SUCCESS
    49,2024-02-14 18:33:59,246.641,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3874,3338,3516,3601,3330,3806,3330,3782,3666,0,3400,5214,5134,5157,0,0x0083,0x0682,0xF887,20.5,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19243,0x0000,0,5352,SUCCESS
    50,2024-02-14 18:34:05,252.626,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3400,5214,5134,5157,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19246,0x0000,0,2168,SUCCESS
    51,2024-02-14 18:34:08,255.781,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3874,3338,3515,3601,3330,3806,3330,3782,3665,0,3399,5216,5134,5157,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19249,0x0000,0,2277,SUCCESS
    52,2024-02-14 18:34:13,260.782,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3399,5216,5134,5157,-1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19254,0x0000,0,2215,SUCCESS
    53,2024-02-14 18:34:18,265.998,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3874,3338,3515,3601,3330,3806,3330,3782,3665,0,3400,5215,5134,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19259,0x0000,0,2255,SUCCESS
    54,2024-02-14 18:34:23,270.806,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3400,5214,5134,5156,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19264,0x0000,0,2264,SUCCESS
    55,2024-02-14 18:34:28,275.812,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3400,5214,5133,5158,2,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,2,13,19269,0x0000,0,2292,SUCCESS
    56,2024-02-14 18:34:33,280.818,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3399,5214,5134,5157,-1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19274,0x0000,0,2174,SUCCESS
    57,2024-02-14 18:34:38,285.997,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3665,0,3399,5214,5134,5158,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19280,0x0000,0,3326,SUCCESS
    58,2024-02-14 18:34:44,291.077,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3874,3338,3515,3601,3330,3805,3330,3782,3665,0,3399,5215,5134,5157,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19284,0x0000,0,2486,SUCCESS
    59,2024-02-14 18:34:49,296.085,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5214,5133,5158,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19289,0x0000,0,2392,SUCCESS
    60,2024-02-14 18:34:54,301.086,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5215,5134,5156,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19294,0x0000,0,2355,SUCCESS
    61,2024-02-14 18:34:59,306.086,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5216,5133,5158,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19299,0x0000,0,2345,SUCCESS
    62,2024-02-14 18:35:04,311.090,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5215,5133,5157,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19304,0x0000,0,2367,SUCCESS
    63,2024-02-14 18:35:09,316.102,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5215,5133,5157,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19309,0x0000,0,2229,SUCCESS
    64,2024-02-14 18:35:14,321.114,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5215,5133,5156,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19314,0x0000,0,2353,SUCCESS
    65,2024-02-14 18:35:19,326.130,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3399,5214,5134,5157,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19319,0x0000,0,2305,SUCCESS
    66,2024-02-14 18:35:24,331.266,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3781,3664,0,3399,5213,5133,5156,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19324,0x0000,0,2180,SUCCESS
    67,2024-02-14 18:35:29,336.443,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3782,3664,0,3398,5213,5134,5157,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19331,0x0000,0,3333,SUCCESS
    68,2024-02-14 18:35:34,341.516,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3781,3663,0,3398,5214,5134,5157,2,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,2,13,19336,0x0000,0,3383,SUCCESS
    69,2024-02-14 18:35:39,346.998,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3873,3338,3514,3601,3330,3805,3330,3781,3664,0,3399,5214,5134,5156,-1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19343,0x0000,0,4884,SUCCESS
    70,2024-02-14 18:35:45,352.453,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3515,3601,3330,3805,3330,3781,3663,0,3399,5215,5133,5157,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19347,0x0000,0,3348,SUCCESS
    71,2024-02-14 18:35:49,357.062,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3514,3601,3330,3805,3330,3781,3663,0,3398,5215,5134,5158,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19350,0x0000,0,2399,SUCCESS
    72,2024-02-14 18:35:54,361.390,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5213,5133,5157,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19355,0x0000,0,2506,SUCCESS
    73,2024-02-14 18:35:59,366.742,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3515,3601,3330,3805,3330,3781,3663,0,3398,5213,5133,5156,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19362,0x0000,0,4620,SUCCESS
    74,2024-02-14 18:36:05,372.096,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3873,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5215,5134,5157,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19366,0x0000,0,2825,SUCCESS
    75,2024-02-14 18:36:09,376.420,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5214,5133,5157,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19370,0x0000,0,2326,SUCCESS
    76,2024-02-14 18:36:14,381.432,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3873,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5213,5133,5157,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19375,0x0000,0,2192,SUCCESS
    77,2024-02-14 18:36:19,386.559,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5213,5133,5156,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.7,20.5,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19380,0x0000,0,2993,SUCCESS
    78,2024-02-14 18:36:24,391.496,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3873,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5214,5133,5157,-1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19385,0x0000,0,2307,SUCCESS
    79,2024-02-14 18:36:29,396.486,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3872,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5213,5133,5156,-2,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-2,13,19390,0x0000,0,2280,SUCCESS
    80,2024-02-14 18:36:34,401.491,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3663,0,3398,5214,5133,5157,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19395,0x0000,0,2201,SUCCESS
    81,2024-02-14 18:36:39,406.603,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3662,0,3398,5213,5133,5157,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.4,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19400,0x0000,0,2248,SUCCESS
    82,2024-02-14 18:36:44,411.508,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3872,3338,3514,3601,3330,3804,3330,3781,3662,0,3398,5213,5133,5156,-1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19405,0x0000,0,2227,SUCCESS
    83,2024-02-14 18:36:49,416.521,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3662,0,3398,5214,5133,5156,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19410,0x0000,0,2235,SUCCESS
    84,2024-02-14 18:36:54,421.527,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3780,3662,0,3398,5213,5133,5156,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19415,0x0000,0,2255,SUCCESS
    85,2024-02-14 18:36:59,426.615,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3780,3662,0,3397,5213,5133,5156,0,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19420,0x0000,0,2393,SUCCESS
    86,2024-02-14 18:37:04,431.545,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3781,3662,0,3397,5213,5133,5155,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19425,0x0000,0,2635,SUCCESS
    87,2024-02-14 18:37:09,436.547,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3872,3338,3514,3601,3330,3804,3330,3781,3662,0,3397,5213,5133,5157,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19430,0x0000,0,2564,SUCCESS
    88,2024-02-14 18:37:14,441.553,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3872,3338,3514,3601,3330,3804,3330,3780,3662,0,3397,5213,5132,5157,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19435,0x0000,0,2569,SUCCESS
    89,2024-02-14 18:37:19,446.727,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3331,3872,3338,3514,3601,3330,3804,3330,3780,3662,0,3397,5212,5133,5156,1,0x0083,0x0682,0xF887,20.6,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,1,13,19440,0x0000,0,2302,SUCCESS
    90,2024-02-14 18:37:24,451.565,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3513,3601,3330,3803,3330,3780,3661,0,3397,5213,5132,5157,-1,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19445,0x0000,0,2289,SUCCESS
    91,2024-02-14 18:37:29,456.569,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3514,3601,3330,3803,3330,3780,3661,1,3397,5213,5132,5156,0,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19450,0x0000,0,2212,SUCCESS
    92,2024-02-14 18:37:34,461.572,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3872,3338,3514,3601,3330,3803,3330,3780,3661,0,3397,5213,5133,5156,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.6,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.7,-273.2,0,0,13,19455,0x0000,0,2301,SUCCESS
    93,2024-02-14 18:37:39,466.744,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3513,3601,3330,3803,3330,3780,3661,0,3397,5213,5132,5156,0,0x0083,0x0682,0xF887,20.9,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19460,0x0000,0,2208,SUCCESS
    94,2024-02-14 18:37:44,471.573,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3331,3872,3338,3513,3601,3330,3803,3330,3780,3661,0,3397,5213,5133,5156,1,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19465,0x0000,0,2205,SUCCESS
    95,2024-02-14 18:37:49,476.583,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3872,3338,3513,3601,3330,3803,3330,3780,3661,0,3397,5212,5132,5156,1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,1,13,19470,0x0000,0,2215,SUCCESS
    96,2024-02-14 18:37:54,481.593,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3333,3329,3332,3330,3330,3872,3338,3513,3601,3330,3803,3330,3780,3661,0,3397,5213,5132,5156,0,0x0083,0x0682,0xF887,20.7,-273.2,-273.2,-273.2,20.3,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,0,13,19475,0x0000,0,2272,SUCCESS
    97,2024-02-14 18:37:59,486.752,0x0000,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x00,0x8184,3332,3329,3332,3330,3330,3871,3339,3513,3601,3330,3803,3330,3780,3661,0,3397,5213,5132,5156,-1,0x0083,0x0682,0xF887,20.8,-273.2,-273.2,-273.2,20.4,24.7,20.4,-59.5,-59.7,-59.7,0x45,0x0050,21.8,-273.2,0,-1,13,19480,0x0000,0,2050,SUCCESS