Field transmitter is a general term that encompasses the common industrial process control systems: pressure, temperature, and flow. While pressure, temperature, and flow transmitters each pose distinct design challenges and considerations, some signal conditioning similarities exist between the three.
A sensor will convert the physical quantity (i.e. pressure, temperature, flow, etc.) into an electrical signal. More often than not, the sensors used to detect the aforementioned physical quantities produce a small differential electrical signal that needs to be amplified (i.e. bridge sensors, thermocouples, etc.). An instrumentation amplifier is used to amplify the signal and perform the differential to a single ended conversion.
Figure 1 - Simplified field transmitter implementation
The amplified signal is then used to create the renowned 4-20mA current output to transport the sensor data to a remote processer. There are several ways to create this 4-20mA output. For example, a common implementation is to take the analog signal from the instrumentation amplifier and convert it to the digital domain using an analog-to-digital converter (ADC). The digital information is processed by a microprocessor that then controls a digital-to-analog converter (DAC). The DAC output is then used to create the 4-20mA current output.
The voltage to current conversion can be done discretely using an op-amp and some external components, but the simplest way is to use a 4-20mA transmitter (XTR) that integrates the op-amp and offers some additional functionality (i.e. excitation currents, reference voltages, error detection flags, etc.). The XTR amplifier can be easily interfaced with a DAC or directly with the instrumentation amplifier as shown in Figure 1.
Table 1 shows some recommended instrumentation amplifiers for interfacing with many pressure, temperature, and flow sensors. The requirements here are high common-mode rejection (CMR), low offset and offset drift, low noise, and low power.
Table 1 - Instrumentation amplifiers for field transmitters
Device |
CMRR (min, G=1000) |
Input offset voltage (max) |
Input offset drift (max) |
Noise density |
Quiescent current (typ) |
100 dB |
100 µV |
2 µV/°C |
21 nV/√Hz |
250 µA |
|
140 dB |
35 µV |
0.4 µV/°C |
8 nV/√Hz |
350 µA |
|
140 dB |
35 µV |
0.4 µV/°C |
7 nV/√Hz |
650 µA |
|
100 dB |
75 µV |
0.3 µV/°C |
50 nV/√Hz |
50 µA |
Table 2 shows some recommended XTR devices for 2 and 3 wire applications. XTRs offer an easy, ready to use solution for creating a 4-20mA transmitter. Also visit [FAQ] How do I choose a 4-20mA transmitter? for more details.
Table 2- XTR devices for field transmitters
Device |
Functionality |
Supply voltage range |
Features |
2 wire |
7.5V – 36V |
5 V regulator and 2.5 V reference |
|
3 wire |
8V – 40V |
Configurable regulator 3V -5 V |
|
3 wire |
10V – 40V |
User selectable current/voltage output, output error flags, thermal protection |
Table 3 shows some recommended op-amps for a discrete implementation of the 4-20mA function. The requirements here are low power, low offset, and offset drift.
Table 3- Op-amps for field transmitters
Device |
Quiescent current (typ) |
Bandwidth |
Input offset voltage (max) |
Offset voltage drift (typ) |
Supply voltage range |
24 µA |
1 MHz |
45 µV |
1.00 µV/°C |
1.7V – 5.5 V |
|
100 µA |
550 kHz |
10 µV |
0.001 µV/°C |
4.5V – 36 V |
|
17 µA |
350 kHz |
10 µV |
0.02 µV/°C |
1.8 V – 5.5 V |
For useful resources, please make sure to check out the following content.
How to Select Amplifiers for Pressure Transmitter Applications
[FAQ] Designing with 4-20mA current loop transmitters (XTRs): FAQ links
[FAQ] How do Instrumentation Amplifiers (INAs) fit into my design?
TI Precision Labs – Instrumentation Amplifier Video Curriculum
TI Precision Labs - Amplifiers: Introduction to 4-20mA current loop transmitters