TMS320F28379D: PWM singnal missing, when Phase shifting
Part Number: TMS320F28379D
Hi,.
I'm using F28379D controller for my application of controlling two full bridge converter. In this, I am using 4-EPWMs. Im keeping EPWM1 as master and which will generate syncout event when EPWM_SYNC_OUT_PULSE_ON_COUNTER_ZERO. The problem I'm facing was (focusing only on EPWM3), when I'm changing the phase shift value from 0 to 1 in TBPHS of EPWM3, it's missing one entire cycle of pulse. I have tried with many variety of values and found that it happens only when I shift from 0 to other values. I have read some E2E forums and TRM, but didn't getting proper solution for this. The configuration which I've used in EPWM3 was given below, have a look at it. Kindly provide me the solution, why it's happening and how to resolve this. Thanks
EPWM3:
// Set-up TBCLK
EPWM_setTimeEPWM3_BASEPeriod(EPWM3_BASE, EPWM_TIMER_TBPRD-1);
EPWM_setPhaseShift(EPWM3_BASE, 0U);
EPWM_setTimeEPWM3_BASECounter(EPWM3_BASE, 0U);
// Set Compare values
EPWM_setCounterCompareValue(EPWM3_BASE,
EPWM_COUNTER_COMPARE_A,
(EPWM_TIMER_TBPRD/2)-1);
EPWM_COUNTER_COMPARE_B,
// Set up counter mode
EPWM_setTimeEPWM3_BASECounterMode(EPWM3_BASE, EPWM_COUNTER_MODE_UP);
EPWM_disablePhaseShiftLoad(EPWM3_BASE);
EPWM_setClockPrescaler(EPWM3_BASE,
EPWM_CLOCK_DIVIDER_1,
EPWM_HSCLOCK_DIVIDER_1);
// Set up shadowing
EPWM_setCounterCompareShadowLoadMode(EPWM3_BASE,
EPWM_COMP_LOAD_ON_CNTR_ZERO);
EPWM_setDeadBandControlShadowLoadMode(EPWM3_BASE, EPWM_DB_LOAD_ON_CNTR_ZERO);
// Set actions
EPWM_setActionQualifierAction(EPWM3_BASE,
EPWM_AQ_OUTPUT_A,
EPWM_AQ_OUTPUT_HIGH,
EPWM_AQ_OUTPUT_ON_TIMEEPWM3_BASE_ZERO);
EPWM_AQ_OUTPUT_B,
EPWM_AQ_OUTPUT_A,
EPWM_AQ_OUTPUT_LOW,
EPWM_AQ_OUTPUT_ON_TIMEEPWM3_BASE_UP_CMPA);
EPWM_AQ_OUTPUT_B,
EPWM_AQ_OUTPUT_LOW,
EPWM_AQ_OUTPUT_ON_TIMEEPWM3_BASE_UP_CMPB);
// ePWM1 SYNCO is generated on CTR=0
EPWM_setSyncOutPulseMode(EPWM1_BASE, EPWM_SYNC_OUT_PULSE_ON_COUNTER_ZERO);
Here i've attached the missing pulse event. Yellow - EPWM3A, Green - EPWM3B both are complementry signals.
  • Hi Karthick,
    When are updating your TBPHS value to 1? I also see that you are disabling phase shift load for EPWM3 in the initialization. You should be sure to enable phase shift loading to implement your phase shift, are you changing this in your ISR where you update TBPHS?
    Allison
  • Hi, Thanks for your quick response.
    Actually I'm changing the phase shift through debugging mode by directly changing the TBPHS register values. Initially it was kept running at 0-phase. Once I change its value to 1, it misses once cycle of pulse then comes to normal condition. And I'm disabling first, then enabling the Enable Phase Load function on EPWM3 after the configuring the peripheral.
    //EPWM FirmWare Source File
    #include "can_fw.h"
    #include "epwm_fw.h"
    #include "config_fw.h"
    #include "driverlib.h"
    #include "device.h"
    #include "SFO_V8.h"
    #include "conv_fw.h"
    #include "sw_timer.h"
    #include "sdfm_fw.h"
    #include "cmpss.h"
    #define EPWM_MAX_DEADBAND_TIME       300U//4840U//4000U //This if for slow start, it will start with max DB then reduce little by little,
                                                             //So that the PWM will increase slowly.Avoid capacitor Current spikes.
    #define EPWM_DEADBAND_STEP_SIZE      10U//10U//100U
    #define EPWM_CLOCK_CYCLE             10U //period in nanoSeconds
    #define EPWM_SHIFT_AMOUNT            7U
    #define EPWM_DEADBAND_VALUE(X)       ((X / EPWM_CLOCK_CYCLE) << EPWM_SHIFT_AMOUNT)
    #define EPWM_PRIM_PW_STEP     20
    #define EPWM_SEC_PW_STEP      20
    #define EPWM_PHASE_SHIFT_STEP  10
    #define EPWM_SHIFT_STEP_SIZE  50U
    #define EPWM_DEFAULT_PHASE_SHIFT 30U
    #define EPWM_ZERO_PHASE_SHIFT  0U
    #define EPWM_GPIO_GD_EN_PRI  9U
    #define EPWM_GPIO_GD_EN_SEC  11U
    #define PWM_COUNT          5
    #define CHANNEL_A          1
    #define CHANNEL_B          2
    #define CHANNEL_AB         3
    #define EPWM_TIMER_TBPRD   1000U
    //Macros for PWM1
    #define EPWM1_TIMER_TBPRD  1000U//to be changed to 5us
    #define EPWM1_CMPA         500U
    #define EPWM1_CMPB         500U
    //Macros for PWM2
    #define EPWM2_TIMER_TBPRD  1000U//to be changed to 5us
    #define EPWM2_CMPA         500U
    #define EPWM2_CMPB         500U
    //Macros for PWM3
    #define EPWM3_TIMER_TBPRD  1000U//300U
    #define EPWM3_CMPA         500U//150U
    #define EPWM3_CMPB         500U//150U
    //Macros for PWM4
    #define EPWM4_TIMER_TBPRD  1000U//300U
    #define EPWM4_CMPA         500U//150U
    #define EPWM4_CMPB         500U//150U
    //Count Mode
    #define EPWM_CMP_UP           1
    #define EPWM_CMP_DOWN         0
    typedef struct
        uint8_t  updateFlag;
        uint8_t  epwmPort;
        uint32_t epwmModule;
        uint16_t epwmPeriod;
        uint16_t epwmTimerIntCount;
        uint16_t epwmCompA;
        uint16_t epwmCompB;
        uint32_t phaseShift;
        uint16_t red;
        uint16_t fed;
    }Epwm_Info_t; //now
    typedef enum
        EPWM_ENABLE_PRIMARY = 0,
        EPWM_ENABLE_SECONDARY,
        EPWM_ENABLE_BOTH,
        EPWM_DISABLE_PRIMARY,
        EPWM_DISABLE_SECONDARY,
        EPWM_DISABLE_BOTH,
    }epwm_switch_control_e;
    typedef enum
        EPWM_IDLE,
        EPWM_STEADY_STATE,
        EPWM_TRIP_STATE,
    }epwm_state_e;
    typedef enum
        PWM_NO_EVENT = 0,
        PWM_START,
        PWM_STABLE,
        PWM_TRIP,
        PWM_STOP,
        PWM_UPDATE_VALUES,
    }epwm_event_e;
    typedef struct
      epwm_state_e state;
      uint16_t counter;	    //Counter was made to take care of slow start period to become stable
      uint16_t deadBand; 	//to keep track of DeadBand value
      uint16_t curr_prim_pulse_ns;	//to keep track of pulse width of Primary( Btw Pwm1 and Pwm2)
      uint16_t curr_sec_pulse_ns;  	//to keep track of pulse width of Secondary( Btw Pwm3 and Pwm4)
      int16_t curr_phase_pri_sec_ns; //to keep track of phase shift between epwm1 and epwm3
      uint16_t final_prim_pulse_ns;   //to track final pulse to be achieved
      uint16_t final_sec_pulse_ns;    //to track final pulse to be achieved
      int16_t final_phase_pri_sec_ns;//to track final phase to be achieved
      int16_t pwm1_time_base;
      int16_t pwm2_time_base;
      int16_t pwm3_time_base;
      int16_t pwm4_time_base;
    }epwm_fw_state_t;
    Epwm_Info_t epwmInfo[PWM_COUNT];
    epwm_fw_state_t epwm_fw_state = {EPWM_IDLE, 0, EPWM_MAX_DEADBAND_TIME, EPWM_ZERO_PHASE_SHIFT};
    volatile uint32_t ePWM[] =
        {0, EPWM1_BASE, EPWM2_BASE, EPWM3_BASE, EPWM4_BASE};
    int MEP_ScaleFactor; // Global variable used by the SFO library
                         // Result can be used for all HRPWM channels
                         // This variable is also copied to HRMSTEP
                         // register by SFO() function.
    /******************************************************** #Init *********************************************************/
    void EPWM_Init(void)
        uint16_t status = 0;
        epwm_ConfigureIOs();
        // Calling SFO() updates the HRMSTEP register with calibrated MEP_ScaleFactor.
        // HRMSTEP must be populated with a scale factor value prior to enabling
        // high resolution period control.
        while(status == SFO_INCOMPLETE)
            status = SFO();
            if(status == SFO_ERROR)
              ESTOP0;
            }              // steps/coarse step exceeds maximum of 255.
        epwm_PreConfigureChannel(EPWM1_BASE);
        epwm_PreConfigureChannel(EPWM2_BASE);
        epwm_PreConfigureChannel(EPWM3_BASE);
        epwm_PreConfigureChannel(EPWM4_BASE);
        // Interrupts that are used in this example are re-mapped to ISR functions
        // found within this file.
        Interrupt_register(INT_EPWM1_TZ, &epwm1TZISR);
        Interrupt_register(INT_EPWM2_TZ, &epwm2TZISR);
        Interrupt_register(INT_EPWM3_TZ, &epwm3TZISR);
        Interrupt_register(INT_EPWM4_TZ, &epwm4TZISR);
        // Assign the interrupt service routines to ePWM interrupts
        // Interrupts commented to avoid frequent interruption
        // earlier used for single pulse
        Interrupt_register(INT_EPWM1, &epwm1_isr);
    //    Interrupt_register(INT_EPWM2, &epwm2_isr);
    //    Interrupt_register(INT_EPWM3, &epwm3_isr);
    //    Interrupt_register(INT_EPWM4, &epwm4_isr);
        // Disable sync(Freeze clock to PWM as well). GTBCLKSYNC is applicable
        // only for multiple core devices. Uncomment the below statement if
        // applicable.
        SysCtl_disablePeripheral(SYSCTL_PERIPH_CLK_TBCLKSYNC);
        epwm_TripZoneInit();
        //Initializing with Maximum Dead-band Time
        epwm_fw_state.deadBand = EPWM_MAX_DEADBAND_TIME;
        // Initialize PWM1 without phase shift as master
        epwm_ConfigureChannel(EPWM1_BASE);
        epwm_HRPWM_DeadBand(1, EPWM_DEADBAND_VALUE(epwm_fw_state.deadBand));
        // Initialize PWM2 with phase shift of 300 TBCLKs
        epwm_ConfigureChannel(EPWM2_BASE);
        EPWM_selectPeriodLoadEvent(EPWM2_BASE, EPWM_SHADOW_LOAD_MODE_SYNC);
        epwm_HRPWM_DeadBand(2, EPWM_DEADBAND_VALUE(epwm_fw_state.deadBand));
        // Initialize PWM3 with phase shift of 600 TBCLKs
        epwm_ConfigureChannel(EPWM3_BASE);
        EPWM_selectPeriodLoadEvent(EPWM3_BASE, EPWM_SHADOW_LOAD_MODE_SYNC);
        epwm_HRPWM_DeadBand(3, EPWM_DEADBAND_VALUE(epwm_fw_state.deadBand));
        // Initialize PWM4 with phase shift of 900 TBCLKs
        epwm_ConfigureChannel(EPWM4_BASE);
        EPWM_selectPeriodLoadEvent(EPWM4_BASE, EPWM_SHADOW_LOAD_MODE_SYNC);
        epwm_HRPWM_DeadBand(4, EPWM_DEADBAND_VALUE(epwm_fw_state.deadBand));
        // ePWM2 uses the ePWM 1 SYNCO as its SYNCIN.
        // ePWM2 SYNCO is generated from its SYNCIN, which is ePWM1 SYNCO
        EPWM_setSyncOutPulseMode(EPWM2_BASE, EPWM_SYNC_OUT_PULSE_ON_EPWMxSYNCIN);
        // ePWM4 uses the ePWM 1 SYNCO as its SYNCIN.
        SysCtl_setSyncInputConfig(SYSCTL_SYNC_IN_EPWM4, SYSCTL_SYNC_IN_SRC_EPWM1SYNCOUT);
        // Enable all phase shifts.
        EPWM_enablePhaseShiftLoad(EPWM2_BASE);
        EPWM_enablePhaseShiftLoad(EPWM3_BASE);
        EPWM_enablePhaseShiftLoad(EPWM4_BASE);
        //to force pwms in tripped state at the time of initialization
        //uncomment below code to run pwms after reset
        EPWM_forceTripZoneEvent(EPWM1_BASE,EPWM_TZ_FORCE_EVENT_OST);
        EPWM_forceTripZoneEvent(EPWM2_BASE,EPWM_TZ_FORCE_EVENT_OST);
        EPWM_forceTripZoneEvent(EPWM3_BASE,EPWM_TZ_FORCE_EVENT_OST);
        EPWM_forceTripZoneEvent(EPWM4_BASE,EPWM_TZ_FORCE_EVENT_OST);
        // Enable sync and clock to PWM
        SysCtl_enablePeripheral(SYSCTL_PERIPH_CLK_TBCLKSYNC);
        epwm_Post_Init();
        //timer used for calling mep calibration function
        sw_timer_start(CONV_FW_MEP_CAL_TIMER_INDEX, CONV_FW_MED_CAL_TIMER_PERIOD_MS, SW_TIMER_PERIODIC);
        //timer used for updating the values into current status of pheripheral
        sw_timer_start(CONV_FW_PWM_UPDATE_TIMER_INDEX, CONV_FW_PWM_UPDATE_TIMER_PERIOD_MS, SW_TIMER_PERIODIC);
    // Configure Output pins and Mux settings for 8 PWMs for gate driver control
    static void epwm_ConfigureIOs(void)
        #ifdef _CONTROL_CARD
        //Primary side gate driver IN-/enable pin configuration as GPIO
        GPIO_setPadConfig(EPWM_GPIO_GD_EN_PRI, GPIO_PIN_TYPE_STD);
        GPIO_setDirectionMode(EPWM_GPIO_GD_EN_PRI, GPIO_DIR_MODE_OUT);
        epwm_Disable_Drivers_Primary();
        GPIO_setPadConfig(EPWM_GPIO_GD_EN_SEC, GPIO_PIN_TYPE_STD);
        GPIO_setDirectionMode(EPWM_GPIO_GD_EN_SEC, GPIO_DIR_MODE_OUT);
        epwm_Disable_Drivers_Secondary();
    #endif /* _CONTROL_CARD */
        // EPWM1 -> EPWM1 Pinmux
        GPIO_setPinConfig(GPIO_0_EPWM1A);
        GPIO_setPadConfig(1, GPIO_PIN_TYPE_STD);
        GPIO_setQualificationMode(1, GPIO_QUAL_SYNC);
        GPIO_setPinConfig(GPIO_1_EPWM1B);
        GPIO_setPadConfig(2, GPIO_PIN_TYPE_STD);
        GPIO_setQualificationMode(2, GPIO_QUAL_SYNC);
        // EPWM2 -> EPWM2 Pinmux
        GPIO_setPinConfig(GPIO_2_EPWM2A);
        GPIO_setPadConfig(3, GPIO_PIN_TYPE_STD);
        GPIO_setQualificationMode(3, GPIO_QUAL_SYNC);
        GPIO_setPinConfig(GPIO_3_EPWM2B);
        GPIO_setPadConfig(4, GPIO_PIN_TYPE_STD);
        GPIO_setQualificationMode(4, GPIO_QUAL_SYNC);
        // EPWM3 -> EPWM3 Pinmux
        GPIO_setPinConfig(GPIO_4_EPWM3A);
        GPIO_setPadConfig(5, GPIO_PIN_TYPE_STD);
        GPIO_setQualificationMode(5, GPIO_QUAL_SYNC);
        GPIO_setPinConfig(GPIO_5_EPWM3B);
        GPIO_setPadConfig(6, GPIO_PIN_TYPE_STD);
        GPIO_setQualificationMode(6, GPIO_QUAL_SYNC);
        // EPWM4 -> EPWM4 Pinmux
        GPIO_setPinConfig(GPIO_6_EPWM4A);
        GPIO_setPadConfig(7, GPIO_PIN_TYPE_STD);
        GPIO_setQualificationMode(7, GPIO_QUAL_SYNC);
        GPIO_setPinConfig(GPIO_7_EPWM4B);
        GPIO_setPadConfig(8, GPIO_PIN_TYPE_STD);
        GPIO_setQualificationMode(8, GPIO_QUAL_SYNC);
    static void epwm_PreConfigureChannel(uint32_t base)
        EPWM_setClockPrescaler(base, EPWM_CLOCK_DIVIDER_1, EPWM_HSCLOCK_DIVIDER_1);
        EPWM_setTimeBasePeriod(base, 0);
        EPWM_setTimeBaseCounter(base, 0);
        EPWM_setTimeBaseCounterMode(base, EPWM_COUNTER_MODE_STOP_FREEZE);
        EPWM_disablePhaseShiftLoad(base);
        EPWM_setPhaseShift(base, 0);
        EPWM_setCounterCompareValue(base, EPWM_COUNTER_COMPARE_A, 0);
        EPWM_setCounterCompareShadowLoadMode(base, EPWM_COUNTER_COMPARE_A, EPWM_COMP_LOAD_ON_CNTR_ZERO);
        EPWM_setCounterCompareValue(base, EPWM_COUNTER_COMPARE_B, 0);
        EPWM_setCounterCompareShadowLoadMode(base, EPWM_COUNTER_COMPARE_B, EPWM_COMP_LOAD_ON_CNTR_ZERO);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_ZERO);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_PERIOD);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_UP_CMPA);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_DOWN_CMPA);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_UP_CMPB);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_A, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_DOWN_CMPB);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_ZERO);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_PERIOD);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_UP_CMPA);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_DOWN_CMPA);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_UP_CMPB);
        EPWM_setActionQualifierAction(base, EPWM_AQ_OUTPUT_B, EPWM_AQ_OUTPUT_NO_CHANGE, EPWM_AQ_OUTPUT_ON_TIMEBASE_DOWN_CMPB);
    static void epwm_TripZoneInit()
        //This is tripping for EPWM1 with Filter3 Using Mux20
        //XBAR configuration for mapping SDFM threshold trigger event to Digital Compare submodule
        //Trip Zone
        //Muxing the trip4 signal to all SDFM Filter Comparators.
        XBAR_setEPWMMuxConfig(XBAR_TRIP4, XBAR_EPWM_MUX16_SD1FLT1_COMPH_OR_COMPL);
        XBAR_enableEPWMMux(XBAR_TRIP4, XBAR_MUX16);
        XBAR_setEPWMMuxConfig(XBAR_TRIP4, XBAR_EPWM_MUX18_SD1FLT2_COMPH_OR_COMPL);
        XBAR_enableEPWMMux(XBAR_TRIP4, XBAR_MUX18);
        XBAR_setEPWMMuxConfig(XBAR_TRIP4, XBAR_EPWM_MUX20_SD1FLT3_COMPH_OR_COMPL);
        XBAR_enableEPWMMux(XBAR_TRIP4, XBAR_MUX20);
        XBAR_setEPWMMuxConfig(XBAR_TRIP4, XBAR_EPWM_MUX22_SD1FLT4_COMPH_OR_COMPL);
        XBAR_enableEPWMMux(XBAR_TRIP4, XBAR_MUX22);
        XBAR_setEPWMMuxConfig(XBAR_TRIP4, XBAR_EPWM_MUX00_CMPSS1_CTRIPH);
        XBAR_enableEPWMMux(XBAR_TRIP4, XBAR_MUX00);
        XBAR_setEPWMMuxConfig(XBAR_TRIP4, XBAR_EPWM_MUX02_CMPSS2_CTRIPH);
        XBAR_enableEPWMMux(XBAR_TRIP4, XBAR_MUX02);
        //////////////////////////------ EPWM1 With TRIPIN4-----//////////////////////////////////////////
        // Select TRIPIN1 (INPUT XBAR INPUT1) as the source for DCAH
        EPWM_selectDigitalCompareTripInput(
                EPWM1_BASE, EPWM_DC_TRIP_TRIPIN4, EPWM_DC_TYPE_DCAH);
        // DCAEVT1 is generated when DCAH is low
        EPWM_setTripZoneDigitalCompareEventCondition(
                EPWM1_BASE, EPWM_TZ_DC_OUTPUT_A1, EPWM_TZ_EVENT_DCXH_HIGH);
        // DCAEVT1 uses the unfiltered version of DCAEVT1
        EPWM_setDigitalCompareEventSource(
                EPWM1_BASE, EPWM_DC_MODULE_A, EPWM_DC_EVENT_1, EPWM_DC_EVENT_SOURCE_ORIG_SIGNAL);
        // DCAEVT1 is asynchronous
        EPWM_setDigitalCompareEventSyncMode(
                EPWM1_BASE, EPWM_DC_MODULE_A, EPWM_DC_EVENT_1, EPWM_DC_EVENT_INPUT_NOT_SYNCED);
        // Action on DCAEVT1
        // Force the EPWMA LOW
        EPWM_setTripZoneAction(EPWM1_BASE,
                               EPWM_TZ_ACTION_EVENT_TZA,
                               EPWM_TZ_ACTION_LOW);
                               EPWM_TZ_ACTION_EVENT_TZB,
        EPWM_enableTripZoneInterrupt(EPWM1_BASE, EPWM_TZ_INTERRUPT_DCAEVT1);
        //////////////////////////------ EPWM2 With TRIPIN4-----//////////////////////////////////////////
                EPWM2_BASE, EPWM_DC_TRIP_TRIPIN4, EPWM_DC_TYPE_DCAH);
                EPWM2_BASE, EPWM_TZ_DC_OUTPUT_A1, EPWM_TZ_EVENT_DCXH_HIGH);
                EPWM2_BASE, EPWM_DC_MODULE_A, EPWM_DC_EVENT_1, EPWM_DC_EVENT_SOURCE_ORIG_SIGNAL);
                EPWM2_BASE, EPWM_DC_MODULE_A, EPWM_DC_EVENT_1, EPWM_DC_EVENT_INPUT_NOT_SYNCED);
        EPWM_setTripZoneAction(EPWM2_BASE,
        EPWM_enableTripZoneInterrupt(EPWM2_BASE, EPWM_TZ_INTERRUPT_DCAEVT1);
        //////////////////////////------ EPWM3 With TRIPIN4-----//////////////////////////////////////////
                EPWM3_BASE, EPWM_DC_TRIP_TRIPIN4, EPWM_DC_TYPE_DCAH);
                EPWM3_BASE, EPWM_TZ_DC_OUTPUT_A1, EPWM_TZ_EVENT_DCXH_HIGH);
                EPWM3_BASE, EPWM_DC_MODULE_A, EPWM_DC_EVENT_1, EPWM_DC_EVENT_SOURCE_ORIG_SIGNAL);
                EPWM3_BASE, EPWM_DC_MODULE_A, EPWM_DC_EVENT_1, EPWM_DC_EVENT_INPUT_NOT_SYNCED);
        EPWM_setTripZoneAction(EPWM3_BASE,
        EPWM_enableTripZoneInterrupt(EPWM3_BASE, EPWM_TZ_INTERRUPT_DCAEVT1);
        //////////////////////////------ EPWM4 With TRIPIN4-----//////////////////////////////////////////
                EPWM4_BASE, EPWM_DC_TRIP_TRIPIN4, EPWM_DC_TYPE_DCAH);
                EPWM4_BASE, EPWM_TZ_DC_OUTPUT_A1, EPWM_TZ_EVENT_DCXH_HIGH);
                EPWM4_BASE, EPWM_DC_MODULE_A, EPWM_DC_EVENT_1, EPWM_DC_EVENT_SOURCE_ORIG_SIGNAL);
                EPWM4_BASE, EPWM_DC_MODULE_A, EPWM_DC_EVENT_1, EPWM_DC_EVENT_INPUT_NOT_SYNCED);
        EPWM_setTripZoneAction(EPWM4_BASE,
        EPWM_enableTripZoneInterrupt(EPWM4_BASE, EPWM_TZ_INTERRUPT_DCAEVT1);
        Interrupt_enable(INT_EPWM1_TZ);
        Interrupt_enable(INT_EPWM2_TZ);
        Interrupt_enable(INT_EPWM3_TZ);
        Interrupt_enable(INT_EPWM4_TZ);
    static void epwm_ConfigureChannel(uint32_t base)
        // Set-up TBCLK
        EPWM_setTimeBasePeriod(base, EPWM_TIMER_TBPRD-1);
        EPWM_setPhaseShift(base, 0U);
        EPWM_setTimeBaseCounter(base, 0U);
        EPWM_setTimeBaseCounterMode(base, EPWM_COUNTER_MODE_UP);
        // Set up shadowing
        EPWM_setDeadBandControlShadowLoadMode(base, EPWM_DB_LOAD_ON_CNTR_ZERO);
        // Set actions
                                      EPWM_AQ_OUTPUT_A,
                                      EPWM_AQ_OUTPUT_B,
                                      EPWM_AQ_OUTPUT_A,
                                      EPWM_AQ_OUTPUT_LOW,
                                      EPWM_AQ_OUTPUT_B,
                                      EPWM_AQ_OUTPUT_LOW,
        HRPWM_setMEPEdgeSelect(base, HRPWM_CHANNEL_A, HRPWM_MEP_CTRL_RISING_AND_FALLING_EDGE);
        HRPWM_setMEPControlMode(base, HRPWM_CHANNEL_A, HRPWM_MEP_DUTY_PERIOD_CTRL);
        HRPWM_setCounterCompareShadowLoadEvent(base, HRPWM_CHANNEL_A, HRPWM_LOAD_ON_CNTR_ZERO_PERIOD);
        HRPWM_setMEPEdgeSelect(base, HRPWM_CHANNEL_B, HRPWM_MEP_CTRL_RISING_AND_FALLING_EDGE);
        HRPWM_setMEPControlMode(base, HRPWM_CHANNEL_B, HRPWM_MEP_DUTY_PERIOD_CTRL);
        HRPWM_setCounterCompareShadowLoadEvent(base, HRPWM_CHANNEL_B, HRPWM_LOAD_ON_CNTR_ZERO_PERIOD);
        HRPWM_enableAutoConversion(base);
        // Turn on high-resolution period control.
        HRPWM_enablePeriodControl(base);
        HRPWM_enablePhaseShiftLoad(base);
        EPWM_forceSyncPulse(base);
        // Interrupt where we will change the Compare Values
        // Select INT on Time base counter zero event,
        // Enable INT, generate INT on 1rd event
        // below code not being used as epwm interrupts are disabled
        EPWM_setInterruptSource(base, EPWM_INT_TBCTR_ZERO);
        EPWM_enableInterrupt(base);
        EPWM_setInterruptEventCount(base, 1U);
    void epwm_Post_Init(void)
        EPWM_enableTripZoneSignals(EPWM1_BASE, EPWM_TZ_SIGNAL_DCAEVT1);
        EPWM_enableTripZoneSignals(EPWM2_BASE, EPWM_TZ_SIGNAL_DCAEVT1);
        EPWM_enableTripZoneSignals(EPWM3_BASE, EPWM_TZ_SIGNAL_DCAEVT1);
        EPWM_enableTripZoneSignals(EPWM4_BASE, EPWM_TZ_SIGNAL_DCAEVT1);
    /******************************************************** #DeadBand *********************************************************/
    // @fn: this will set DeadBand value with Active High RED on Both channels
    // @param: base contains base value for DB to set. value contains actual value to set in (DBRED:DBREDHR)
    // \b Note: redCount is a 21 bit value.
    // \b Note: For configuring DBRED = 0x4, DBREDHR = 0x1; value of
    //          redCount = ((0x4 << 7) | 0x1) = 0x201
    static void epwm_HRPWM_DeadBand(uint8_t base, uint32_t value)
        // DO NOT Switch Output A with Output B
        // true - it will swap the signal , ie. it will replicate other channel's signal
        // false -  it will produce same signal as it generates
        //@must - during complementary mode, these lines will set the swap mode, if we do these steps after setting up
        //        then our output might have some problems. so do this at beginning of init.
        EPWM_setDeadBandOutputSwapMode(ePWM[base], EPWM_DB_OUTPUT_A, false);
        EPWM_setDeadBandOutputSwapMode(ePWM[base], EPWM_DB_OUTPUT_B, false);
        // Use EPWMA as the input for both RED and FED
        EPWM_setRisingEdgeDeadBandDelayInput(ePWM[base], EPWM_DB_INPUT_EPWMA);
        EPWM_setFallingEdgeDeadBandDelayInput(ePWM[base], EPWM_DB_INPUT_EPWMB);
        // Set the RED and FED values
        HRPWM_setRisingEdgeDelay(ePWM[base], value);
        HRPWM_setFallingEdgeDelay(ePWM[base], value);
        // Invert only the Falling Edge delayed output (AHC)
        //EPWM_DB_POLARITY_ACTIVE_HIGH - It will produce same signal as mentioned DB
        //EPWM_DB_POLARITY_ACTIVE_LOW - It will produce complement of the signal
        EPWM_setDeadBandDelayPolarity(ePWM[base], EPWM_DB_RED, EPWM_DB_POLARITY_ACTIVE_HIGH);
        EPWM_setDeadBandDelayPolarity(ePWM[base], EPWM_DB_FED, EPWM_DB_POLARITY_ACTIVE_LOW);
        // Use the delayed signals instead of the original signals
        EPWM_setDeadBandDelayMode(ePWM[base], EPWM_DB_RED, true);
        EPWM_setDeadBandDelayMode(ePWM[base], EPWM_DB_FED, true);
        HRPWM_setDeadbandMEPEdgeSelect(ePWM[base], HRPWM_DB_MEP_CTRL_RED_FED);
        HRPWM_setRisingEdgeDelayLoadMode(ePWM[base], HRPWM_LOAD_ON_CNTR_ZERO);
        HRPWM_setFallingEdgeDelayLoadMode(ePWM[base], HRPWM_LOAD_ON_CNTR_ZERO);
        TRACE_I(EPWM_TRACE,"EPWM%d Setted FED & RED with value = %d ...\r\n",(uint32_t)base,value);
    /******************************************************** #Phase Shift *********************************************************/
    void Epwm_Fw_SetPhaseShifts(uint16_t priShift, int16_t pri_sec_shift, uint16_t secShift)
        int16_t phase12 = priShift - epwm_fw_state.pwm1_time_base;
        int16_t phase13 = pri_sec_shift + phase12/2 - secShift/2;
        int16_t phase14 = pri_sec_shift + phase12/2 + secShift/2;
        if(phase12 <= 5000 && phase13 <= 5000 && phase14 <= 7500 && phase14 >= phase13)
            epwm_fw_state.curr_prim_pulse_ns = priShift;
            epwm_fw_state.curr_sec_pulse_ns = secShift;
            epwm_fw_state.curr_phase_pri_sec_ns = pri_sec_shift;
            Epwm_Fw_SetPhase12(phase12);
            Epwm_Fw_SetPhase13(phase13);
            Epwm_Fw_SetPhase14(phase14);
    //It will alter Pulse width of Primary,
    //sets phase shift on EPWM2 alone (Shift Btw Pwm1 and Pwm2)
    void Epwm_Fw_SetPulseWidthPri(int16_t shiftValue)
        int16_t pulse = shiftValue - epwm_fw_state.pwm1_time_base;
        int16_t phase13 = epwm_fw_state.curr_phase_pri_sec_ns + pulse/2 - epwm_fw_state.curr_sec_pulse_ns/2;
        int16_t phase14 = epwm_fw_state.curr_phase_pri_sec_ns + pulse/2 + epwm_fw_state.curr_sec_pulse_ns/2;
        if(pulse <= 5000 && phase13 <= 5000 && phase14 <= 7500)
            epwm_fw_state.curr_prim_pulse_ns = pulse;
            Epwm_Fw_SetPhase12(shiftValue);
    //It will alter Pulse width of Secondary,
    //sets phase shift on Pmw3 and Pwm4 alone (Shift Btw Pwm3 and Pwm4)
    void Epwm_Fw_SetPulseWidthSec(int16_t shiftValue)
        int16_t phase13 = epwm_fw_state.curr_phase_pri_sec_ns + epwm_fw_state.curr_prim_pulse_ns/2 - shiftValue/2;
        int16_t phase14 = epwm_fw_state.curr_phase_pri_sec_ns + epwm_fw_state.curr_prim_pulse_ns/2 + shiftValue/2;
        if(phase13 <= 5000 && phase14 <= 7500)
            epwm_fw_state.curr_sec_pulse_ns = phase14 - phase13;
    //It will set the Phase shift between Primary to Secondary
    void Epwm_Fw_SetPhaseShift_Pri_Sec(int16_t value)
        int16_t phase13 = value + epwm_fw_state.curr_prim_pulse_ns/2 - epwm_fw_state.curr_sec_pulse_ns/2;
        int16_t phase14 = value + epwm_fw_state.curr_prim_pulse_ns/2 + epwm_fw_state.curr_sec_pulse_ns/2;
        if(phase13 <= 5000 && phase14 <= 7500 && phase14 >= phase13)
            epwm_fw_state.curr_phase_pri_sec_ns = value;
    //It will set Phase shift on PWM2 w.r.t PWM1
    void Epwm_Fw_SetPhase12(int16_t value)
    //    epwm_fw_state.pwm2_time_base = value;
        uint32_t shift2Count = (EPWM_TIMER_TBPRD - (value/10))%EPWM_TIMER_TBPRD;
        uint8_t shift2CountHr = 0;
        shift2Count <<= 8;
        shift2Count += shift2CountHr;
    //    HRPWM_setPhaseShift(EPWM2_BASE, shift2Count);
        epwmInfo[2].phaseShift = shift2Count;
        epwmInfo[2].updateFlag = TRUE;
    //It will set Phase shift on PWM3 w.r.t PWM1
    void Epwm_Fw_SetPhase13(int16_t value)
        epwm_fw_state.pwm3_time_base = value;
        uint32_t shift3Count = (EPWM_TIMER_TBPRD - (value/10))%EPWM_TIMER_TBPRD;
        uint8_t shift3CountHr = 0;
        shift3Count <<= 8;
        shift3Count += shift3CountHr;
    //    HRPWM_setPhaseShift(EPWM3_BASE, shift3Count);
        epwmInfo[3].phaseShift = shift3Count;
        epwmInfo[3].updateFlag = TRUE;
    //It will set Phase shift on PWM4 w.r.t PWM1
    void Epwm_Fw_SetPhase14(int16_t value)
        epwm_fw_state.pwm4_time_base = value;
        uint32_t shift4Count = (EPWM_TIMER_TBPRD - (value/10))%EPWM_TIMER_TBPRD;
        uint8_t shift4CountHr = 0;
        shift4Count <<= 8;
        shift4Count += shift4CountHr;
    //    HRPWM_setPhaseShift(EPWM4_BASE, shift4Count);
        epwmInfo[4].phaseShift = shift4Count;
        epwmInfo[4].updateFlag = TRUE;
    //todo - implement using soft timer
    void Epwm_Fw_mepCalibration(void)
        uint16_t status = SFO(); // in background, MEP calibration module
                                 // continuously updates MEP_ScaleFactor
        if (sw_timer_process(CONV_FW_MEP_CAL_TIMER_INDEX) == 1)
                if (status == 2)
                    ESTOP0;   // SFO function returns 2 if an error occurs & #
                    // of MEP steps/coarse step
    void Conv_Fw_UpdateValues()
      Epwm_Fw_ReadValues(epwm_values);
       if((epwm_values[2].updateFlag && epwm_values[3].updateFlag && epwm_values[4].updateFlag) == TRUE)
          HWREG(EPWM2_BASE + HRPWM_O_TBPHS) = epwm_values[2].phaseShift << 8U;
          HWREG(EPWM3_BASE + HRPWM_O_TBPHS) = epwm_values[3].phaseShift << 8U;
          HWREG(EPWM4_BASE + HRPWM_O_TBPHS) = epwm_values[4].phaseShift << 8U;
    // epwm1TZISR - ePWM1 TZ ISR
    __interrupt void epwm1TZISR(void)
        // re-enable the interrupts
        EPWM_clearTripZoneFlag(EPWM1_BASE, EPWM_TZ_INTERRUPT | EPWM_TZ_FLAG_DCAEVT1);
        // Uncomment the below lines of code to re-enable
        // the interrupts and the ePWM output if using one-shot
        // Below interrupt to be handled by application
        // todo - implement callback to application
        // EPWM_clearTripZoneFlag(EPWM1_BASE, EPWM_TZ_FLAG_OST | EPWM_TZ_INTERRUPT | EPWM_TZ_FLAG_DCAEVT1);
        // Acknowledge this interrupt to receive more interrupts from group 2.3
    //    Interrupt_clearACKGroup(INTERRUPT_ACK_GROUP2);
    // epwm2TZISR - ePWM2 TZ ISR
    __interrupt void epwm2TZISR(void)
    //    // Uncomment the below lines of code to re-enable the interrupts
        EPWM_clearTripZoneFlag(EPWM2_BASE, EPWM_TZ_INTERRUPT | EPWM_TZ_FLAG_DCAEVT1);
    //    // the interrupts and the ePWM output if using one-shot
    //    EPWM_clearTripZoneFlag(EPWM2_BASE, EPWM_TZ_FLAG_OST | EPWM_TZ_INTERRUPT | EPWM_TZ_FLAG_DCAEVT1);
    //    // Acknowledge this interrupt to receive more interrupts from group 2.3
    // epwm3TZISR - ePWM1 TZ ISR
    __interrupt void epwm3TZISR(void)
        EPWM_clearTripZoneFlag(EPWM3_BASE, EPWM_TZ_INTERRUPT | EPWM_TZ_FLAG_DCAEVT1);
    //    EPWM_clearTripZoneFlag(EPWM3_BASE, EPWM_TZ_FLAG_OST | EPWM_TZ_INTERRUPT | EPWM_TZ_FLAG_DCAEVT1);
    // epwm4TZISR - ePWM1 TZ ISR
    __interrupt void epwm4TZISR(void)
        EPWM_clearTripZoneFlag(EPWM4_BASE, EPWM_TZ_INTERRUPT | EPWM_TZ_FLAG_DCAEVT1);
    //    EPWM_clearTripZoneFlag(EPWM4_BASE, EPWM_TZ_FLAG_OST | EPWM_TZ_INTERRUPT | EPWM_TZ_FLAG_DCAEVT1);
    // epwm1_isr - ePWM 1 _isr
    __interrupt void epwm1_isr(void) //ISR generated for every time period (10uS)
        // Clear INT flag for this timer
        EPWM_clearEventTriggerInterruptFlag(EPWM1_BASE);
        // Acknowledge interrupt group
        Interrupt_clearACKGroup(INTERRUPT_ACK_GROUP3);
    // epwm2_isr - ePWM 2 _isr
    __interrupt void epwm2_isr(void)
        EPWM_clearEventTriggerInterruptFlag(EPWM2_BASE);
    // epwm3_isr - ePWM 3 _isr
    __interrupt void epwm3_isr(void)
        EPWM_clearEventTriggerInterruptFlag(EPWM3_BASE);
    // epwm4_isr - ePWM 4 _isr
    __interrupt void epwm4_isr(void)
        EPWM_clearEventTriggerInterruptFlag(EPWM4_BASE);
    void Epwm_Fw_StepIncPriPulse(void)
        volatile int16_t pulse = 20 + epwm_fw_state.final_prim_pulse_ns;
        if(pulse <= 5000)
            Epwm_Fw_SetPriPulseFinal(pulse);
    //        Epwm_Fw_SetPulseWidthPri(pulse);
    void Epwm_Fw_StepDecPriPulse(void)
        int16_t pulse = epwm_fw_state.final_prim_pulse_ns;
        if(pulse >= 0)
    void Epwm_Fw_StepIncSecPulse(void)
        int16_t pulse = 20 + epwm_fw_state.final_sec_pulse_ns;
        if(pulse <= 5000)
            Epwm_Fw_SetSecPulseFinal(pulse);
    //        Epwm_Fw_SetPulseWidthSec(pulse);
    void Epwm_Fw_StepDecSecPulse(void)
        int16_t pulse = epwm_fw_state.final_sec_pulse_ns;
        if(pulse >= 0)
    //While changing phase shift, first call secondary pulse width function, then change phase.
    void Epwm_Fw_StepIncPhase(void)
        int16_t phase = epwm_fw_state.final_phase_pri_sec_ns + 10;
        if(phase <= 2500)
            Epwm_Fw_Set_Pri_Sec_PhaseFinal(phase);
    //        Epwm_Fw_SetPhaseShift_Pri_Sec(phase);
    void Epwm_Fw_StepDecPhase(void)
        int16_t phase = epwm_fw_state.final_phase_pri_sec_ns - 10;
        if(phase >= 0)
    void Epwm_Fw_SetDeadBandAll(uint16_t value)
        uint8_t base = 0;
        for(base = 1; base <= PWM_COUNT; base++)
            Epwm_Fw_SetRED(base, value);
            Epwm_Fw_SetFED(base, value);
    void Epwm_Fw_StepIncAll(void)
        int16_t value12 = epwm_fw_state.final_prim_pulse_ns + EPWM_PRIM_PW_STEP;
        int16_t value14 = epwm_fw_state.final_sec_pulse_ns + EPWM_SEC_PW_STEP;
        int16_t value13 = epwm_fw_state.final_phase_pri_sec_ns + EPWM_PHASE_SHIFT_STEP;
        if((value12 <= 5000) && (value13 <= 2500 && value13 >= EPWM_DEFAULT_PHASE_SHIFT) && (value14 <= 5000))
            Epwm_Fw_Set_SetPhaseShiftsFinal(value12,value13,value14); //will set all values in final value struct
    void Epwm_Fw_StepDecAll(void)
        int16_t value12 = epwm_fw_state.final_prim_pulse_ns - EPWM_PRIM_PW_STEP;
        int16_t value14 = epwm_fw_state.final_sec_pulse_ns - EPWM_SEC_PW_STEP;
        int16_t value13 = epwm_fw_state.final_phase_pri_sec_ns - EPWM_PHASE_SHIFT_STEP;
    void Epwm_Fw_StepIncDeadBand(void)
        int16_t value = epwm_fw_state.deadBand;
        value += 10;
        if(value <= 500)
            Epwm_Fw_SetDeadBandAll(value);
    void Epwm_Fw_StepDecDeadBand(void)
        value -= 10;
        if(value >= 150)
    void Epwm_Fw_Read(uint8_t* buff)
        buff[2] = epwm_fw_state.curr_prim_pulse_ns >> 8;
        buff[3] = epwm_fw_state.curr_prim_pulse_ns & 0x00FF;
        buff[4] = epwm_fw_state.curr_phase_pri_sec_ns >> 8;
        buff[5] = epwm_fw_state.curr_phase_pri_sec_ns & 0x00FF;
        buff[6] = epwm_fw_state.curr_sec_pulse_ns >> 8;
        buff[7] = epwm_fw_state.curr_sec_pulse_ns & 0x00FF;
    int16_t Epwm_Fw_GetPulseWidthPri()
        return epwm_fw_state.curr_prim_pulse_ns;
    int16_t Epwm_Fw_GetPulseWidthSec()
        return epwm_fw_state.curr_sec_pulse_ns;
    int16_t Epwm_Fw_GetPhaseShift()
        return epwm_fw_state.curr_phase_pri_sec_ns;
    void Epwm_Fw_ReadValues(Epwm_Values_t epwm_values[])
        epwm_values[2].phaseShift = epwmInfo[2].phaseShift;
        epwm_values[2].updateFlag = epwmInfo[2].updateFlag;
        epwmInfo[2].updateFlag = FALSE;
        epwm_values[3].phaseShift = epwmInfo[3].phaseShift;
        epwm_values[3].updateFlag = epwmInfo[3].updateFlag;
        epwmInfo[3].updateFlag = FALSE;
        epwm_values[4].phaseShift = epwmInfo[4].phaseShift;
        epwm_values[4].updateFlag = epwmInfo[4].updateFlag;
        epwmInfo[4].updateFlag = FALSE;
    void Epwm_Fw_SetPhaseAll(uint16_t pri_pw, uint16_t sec_pw, uint16_t pri_sec_phase)
        epwm_fw_state.final_prim_pulse_ns = pri_pw;
        epwm_fw_state.final_sec_pulse_ns = sec_pw;
        epwm_fw_state.final_phase_pri_sec_ns = pri_sec_phase;
    void Epwm_Fw_SetPriPulseFinal(uint16_t pri_pw)
    void Epwm_Fw_SetSecPulseFinal(uint16_t sec_pw)
    void Epwm_Fw_Set_Pri_Sec_PhaseFinal(int16_t pri_sec_phase)
    //will update all final phase shift variables
    void Epwm_Fw_Set_SetPhaseShiftsFinal(uint16_t pri_pw, int16_t pri_sec_phase, uint16_t sec_pw)
    //to update all phase values to current status variables in struct
    void Epwm_Fw_UpdatePhase(void)
        int8_t pri_step = 0, sec_step = 0, phase = 0;
        uint8_t updateFlag = 0;
        int16_t priPulse = epwm_fw_state.curr_prim_pulse_ns;
        int16_t secPulse = epwm_fw_state.curr_sec_pulse_ns;
        int16_t pri_sec_phase = epwm_fw_state.curr_phase_pri_sec_ns;
        if(epwm_fw_state.final_prim_pulse_ns != priPulse)
            updateFlag = 1;
            //will check when final value is more than next step of current value
            if(epwm_fw_state.final_prim_pulse_ns > priPulse + EPWM_PRIM_PW_STEP)
                pri_step += EPWM_PRIM_PW_STEP;
            //will check when final value is less than next step of current value
            else if(epwm_fw_state.final_prim_pulse_ns < priPulse - EPWM_PRIM_PW_STEP)
                pri_step -= EPWM_PRIM_PW_STEP;
            //when step value is larger than difference between final and current
            else
                pri_step = epwm_fw_state.final_prim_pulse_ns - priPulse;
            if (priPulse + pri_step >= 0 && priPulse <= 5000)
    //            Epwm_Fw_SetPulseWidthPri(priPulse + pri_step);
                priPulse += pri_step;
            else
                /* error */
        if(epwm_fw_state.final_sec_pulse_ns != epwm_fw_state.curr_sec_pulse_ns)
            updateFlag = 1;
            if(epwm_fw_state.final_sec_pulse_ns > secPulse + EPWM_SEC_PW_STEP)
                sec_step += EPWM_SEC_PW_STEP;
            else if(epwm_fw_state.final_sec_pulse_ns < secPulse - EPWM_SEC_PW_STEP)
                sec_step -= EPWM_SEC_PW_STEP;
            //when the step value is larger than difference between final and current
            else
                sec_step = epwm_fw_state.final_sec_pulse_ns - secPulse;
            if (secPulse + sec_step >= 0 && secPulse <= 5000)
    //            Epwm_Fw_SetPulseWidthSec(secPulse + sec_step);
                secPulse += sec_step;
            else
                /* error */
        if(epwm_fw_state.final_phase_pri_sec_ns != pri_sec_phase)
            updateFlag = 1;
            if(epwm_fw_state.final_phase_pri_sec_ns > pri_sec_phase + EPWM_PHASE_SHIFT_STEP)
                phase += EPWM_PHASE_SHIFT_STEP;
            else if(epwm_fw_state.final_phase_pri_sec_ns < pri_sec_phase - EPWM_PHASE_SHIFT_STEP)
                phase -= EPWM_PHASE_SHIFT_STEP;
            //when the step change is larger than the difference between final and current
            else
                phase = epwm_fw_state.final_phase_pri_sec_ns - pri_sec_phase;
            if (pri_sec_phase + phase >= 0 && pri_sec_phase <= 2500)
    //            Epwm_Fw_SetPhaseShift_Pri_Sec(pri_sec_phase + phase);
                pri_sec_phase += phase;
            else
                /* error */
        if(updateFlag == TRUE)
            Epwm_Fw_SetPhaseShifts(priPulse, pri_sec_phase, secPulse);
    I'm attaching the configuration file which I've used.
  • Hi Karthick,
    Thanks for sharing your .c code; I see you are using HRPWM as well now. It looks like you are setting the EPWM modules to be in up-count while implementing HR deadband module, is that correct? There is a note in the device TRM section 15.14.1.6 Deadband High-Resolution Operation that states "In up-count mode, the dead-band module is not available when any high-resolution mode is enabled." So I would recommend switching to up-down count mode instead for this application if you are not doing so. There is also another note in section 15.7.2 Dead-band Submodule Additional Operating Modes stating "High-resolution dead-band RED and FED requires Half-Cycle clocking mode (DBCTL[HALFCYCLE] = 1)", so please look into this as well. If you are going to use up-down count, you should also ensure that if you are using HR time base period control, CMPA/B must have shadow loading enabled for when 'TBCTR = 0 or PRD'.
    Let me know if I am misunderstanding your program so far or if you need clarification here as well.
    Allison
  • Hi, Thanks for the reply.
        I've configured as HRPWM in my code, but I'm not using any HRPWM functionalities. But, however this time I've disabled all HRPWM from the code and checked the PWMs. But, I'm facing the same issue this time too. My observation was, when doing in debugger mode. When, I'm changing the TBPHS from higher value to lower value, I'm observed there's a missing of pulse, with their difference (High_value - Low_value). I've share some images with changing phase shift from different values. Can you please check what I'm doing wrong and suggest a proper way of doing. I've attached the new .C code.
    #include "can_fw.h"
    #include "device.h"
    #include "SFO_V8.h"
    #include "cmpss.h"
    #define PWM_COUNT          5
    #define CHANNEL_A          1
    #define CHANNEL_B          2
    //Macros for PWM1
    //Macros for PWM2
    //Macros for PWM3
    //Macros for PWM4
    //Count Mode
    typedef struct
        uint8_t  updateFlag;
        uint8_t  epwmPort;
        uint16_t epwmCompA;
        uint16_t epwmCompB;
        uint16_t red;
        uint16_t fed;
    }Epwm_Info_t; //now
    typedef enum
        EPWM_ENABLE_BOTH,
        EPWM_DISABLE_BOTH,
    typedef enum
        EPWM_IDLE,
        EPWM_STEADY_STATE,
        EPWM_TRIP_STATE,
    }epwm_state_e;
    typedef enum
        PWM_NO_EVENT = 0,
        PWM_START,
        PWM_STABLE,
        PWM_TRIP,
        PWM_STOP,
        PWM_UPDATE_VALUES,
    }epwm_event_e;
    typedef struct
      epwm_state_e state;
    }epwm_fw_state_t;
            status = SFO();
              ESTOP0;
        // applicable.
        // SysCtl_disablePeripheral(SYSCTL_PERIPH_CLK_GTBCLKSYNC);
        // Enable ePWM interrupts
        // Interrupts not being used
    //    Interrupt_enable(INT_EPWM1);
    //    Interrupt_enable(INT_EPWM2);
    //    Interrupt_enable(INT_EPWM3);
    //    Interrupt_enable(INT_EPWM4);
        epwm_Post_Init();
    //*********************#Driver_Enable****************************//
    //function to disable primary side gate driver -> IN- high
    static void epwm_Disable_Drivers_Primary(void)
        GPIO_writePin(EPWM_GPIO_GD_EN_PRI, 1);
    //function to enable primary side gate driver -> IN- low
    static void epwm_Enable_Drivers_Primary(void)
        GPIO_writePin(EPWM_GPIO_GD_EN_PRI, 0);
    //function to disable secondary side gate driver -> IN- high
    static void epwm_Disable_Drivers_Secondary(void)
        GPIO_writePin(EPWM_GPIO_GD_EN_SEC, 1);
    //function to enable secondary side gate driver -> IN- low
    static void epwm_Enable_Drivers_Secondary(void)
        GPIO_writePin(EPWM_GPIO_GD_EN_SEC, 0);
    //*********************#Driver_Enable_End****************************//
        //Trip Zone
        // Set-up TBCLK
        // Set up shadowing
        // Set actions
                                      EPWM_AQ_OUTPUT_A,
                                      EPWM_AQ_OUTPUT_B,
                                      EPWM_AQ_OUTPUT_A,
                                      EPWM_AQ_OUTPUT_LOW,
                                      EPWM_AQ_OUTPUT_B,
                                      EPWM_AQ_OUTPUT_LOW,
        EPWM_enablePhaseShiftLoad(base);
    //    EPWM_setDeadBandCounterClock(base,EPWM_DB_COUNTER_CLOCK_HALF_CYCLE);
        EPWM_setRisingEdgeDelayCount(ePWM[base], value);
        EPWM_setFallingEdgeDelayCount(ePWM[base], value);
        EPWM_setRisingEdgeDelayCountShadowLoadMode(ePWM[base], EPWM_RED_LOAD_ON_CNTR_ZERO);
        EPWM_setFallingEdgeDelayCountShadowLoadMode(ePWM[base], EPWM_FED_LOAD_ON_CNTR_ZERO);
    //! \b Note: redCount is a 21 bit value.
    //! \b Note: For configuring DBRED = 0x4, DBREDHR = 0x1; value of
    //!          redCount = ((0x4 << 7) | 0x1) = 0x201
    void Epwm_Fw_SetRED(uint8_t base, uint16_t value)  //value will be in nS
       epwm_fw_state.deadBand = value;
       uint16_t redCount = ((uint16_t)(value/10));    //converting nS into step counts for EPWM
       uint8_t redCountHr = 0;
    // redCountHr = (uint8_t)((value%10)*5.55);    //converting the nS into MEP steps for HRDB -> 1nS = 5.55steps(1step = 180pS)
       redCount +=redCountHr;
       EPWM_setRisingEdgeDelayCount(ePWM[base], redCount);
       epwmInfo[base].red = redCount;
       epwmInfo[base].updateFlag = TRUE;
    //! \b Note: fedCount is a 21 bit value.
    //! \b Note: For configuring DBFED = 0x4, DBFEDHR = 0x1; value of
    //!          fedCount = ((0x4 << 7) | 0x1) = 0x20
    void Epwm_Fw_SetFED(uint8_t base, uint16_t value)  //value will be in nS
       uint16_t fedCount = ((uint16_t)(value/10));    //converting nS into step counts for EPWM
       uint8_t fedCountHr = 0;
    //   fedCountHr = (uint8_t)((value%10)*5.55);    //converting the nS into MEP steps for HRDB -> 1nS = 5.55steps(1step = 180pS)
       fedCount +=fedCountHr;
       EPWM_setFallingEdgeDelayCount(ePWM[base], fedCount);
       epwmInfo[base].fed = fedCount;
        shift2Count <<= 8;
        shift3Count <<= 8;
        shift4Count <<= 8;
                if (status == 2)
    /******************************************************** #Control PWM *********************************************************/
    void Epwm_Fw_EnablePrimarySignal(void)
    //    Epwm_Fw_SetPriPulse(EPWM_ZERO_PHASE_SHIFT);
    //    Epwm_Fw_SetSecPulse(EPWM_ZERO_PHASE_SHIFT);
    //    Epwm_Fw_Set_Pri_Sec_Phase(EPWM_ZERO_PHASE_SHIFT);
        Epwm_Fw_Set_SetPhaseShiftsFinal(EPWM_ZERO_PHASE_SHIFT, EPWM_DEFAULT_PHASE_SHIFT, EPWM_ZERO_PHASE_SHIFT);
        if(Sdfm_Fw_Process(SDFM_ENABLE_PROTECTION) == SUCCESS)
        	Epwm_Fw_Process(PWM_START);
            EPWM_clearTripZoneFlag(EPWM1_BASE, EPWM_TZ_FLAG_OST);
            EPWM_clearTripZoneFlag(EPWM2_BASE, EPWM_TZ_FLAG_OST);
            epwm_Enable_Drivers_Primary();
    void Epwm_Fw_EnableSecondarySignal(void)
            EPWM_clearTripZoneFlag(EPWM3_BASE, EPWM_TZ_FLAG_OST);
            EPWM_clearTripZoneFlag(EPWM4_BASE, EPWM_TZ_FLAG_OST);
            epwm_Enable_Drivers_Secondary();
    void Epwm_Fw_EnableBothSignal(void)
    void Epwm_Fw_DisablePrimarySignal(void)
        Epwm_Fw_Process(PWM_STOP);
    void Epwm_Fw_DisableSecondarySignal(void)
    void Epwm_Fw_DisableBothSignal(void)
        if(pulse <= 5000)
        if(pulse >= 0)
        if(pulse <= 5000)
        if(pulse >= 0)
        if(phase <= 2500)
        if(phase >= 0)
        uint8_t base = 0;
        value += 10;
        if(value <= 500)
        value -= 10;
        if(value >= 150)
            updateFlag = 1;
            else
            else
                /* error */
            updateFlag = 1;
            else
            else
                /* error */
            updateFlag = 1;
            else
            else
                /* error */
    Note: Time period of PWM is 10uS. Duty is 50% (5uS). Yellow - PWM3A, Green - PWM3B
    1. Phase shift value in TBPHS: changed from 999 to 1
    2. Phase shift value in TBPHS: changed from 999 to 750
    3. Phase shift value in TBPHS: changed from 750 to 1
    4. Phase shift value in TBPHS: changed from 900 to 800
    Thanks.
  • Hi Karthick,
    Missing pulses and longer high pulses can sometimes occur due to the order of events as well as the TBPHS value you are switching to - which can cause missing action qualifiers. Here is a brief explanation of this happening on another thread: https://e2e.ti.com/support/microcontrollers/c2000-microcontrollers-group/c2000/f/c2000-microcontrollers-forum/1185529/tms320f280049c-the-first-period-of-the-output-waveform-is-abnormal-after-the-pwm-phase-shift-value-changes-from-0-to-non-0?tisearch=e2e-sitesearch&keymatch=missing%2525252520pulse%2525252520phase%2525252520shift#.
    Since you are in up-count mode, keep in mind CTR=PRD and CTR=0 occur together as well. In the explanation from that other thread I listed, you will note that this pulse behavior is expected (and it is harder to tell if there is actually an issue here since you are changing the TBPHS value directly in registers during debugger mode and we don't know when exactly this is implemented in the flow of events as opposed to updating it at some fixed time).
    Are you trying to update the TBPHS value at some fixed/known time/ISR and still seeing an issue occur? Or is it only when you are changing the TBPHS value manually in debugging mode?
    Allison
  • Hi, Sorry for the delay. Thank you for your suggestions. I've gone through the threads which you've shared. Now, I've managed to take actions on the missing pulse, during the compare events. But, while testing the code now I found one more issue. This was not expected and I didn't get any idea why it's happening.
    In my code I'm using Up-Down count mode with Period of 500. I've compare events such as CMPA = CMPB = 250. AQ Events are, PWM4A HIGH when Up-CMPA and PWM4A LOW when Down-CMPB. By default, it's down count after sync. The issue I'm facing was when I'm going TBPHS value from 499 to 500, I'm facing the same missing pulse. I don't know what causing the signal to not going low, the PWMA signal is high for one entire cycle. I've attached my code and snap of the oscilloscope image also. Can you please find the issue and why is that strange thing is happening. Thanks
    #include "can_fw.h"
    #include "device.h"
    #include "SFO_V8.h"
    #include "cmpss.h"
            status = SFO();
              ESTOP0;
    //    Interrupt_register(INT_EPWM1, &epwm1_isr);
        // applicable.
        epwm_Post_Init();
        // Set-up TBCLK
        EPWM_setTimeBasePeriod(base, EPWM_TIMER_TBPRD);
                                    (EPWM_TIMER_TBPRD/2));
        EPWM_setTimeBaseCounterMode(base, EPWM_COUNTER_MODE_UP_DOWN);
        // Set up shadowing
                                             EPWM_COMP_LOAD_ON_CNTR_ZERO_PERIOD);
        EPWM_setDeadBandControlShadowLoadMode(base, EPWM_DB_LOAD_ON_CNTR_ZERO_PERIOD);
        // Set actions
                                      EPWM_AQ_OUTPUT_A,
                                      EPWM_AQ_OUTPUT_B,
                                      EPWM_AQ_OUTPUT_A,
                                      EPWM_AQ_OUTPUT_LOW,
                                      EPWM_AQ_OUTPUT_B,
                                      EPWM_AQ_OUTPUT_LOW,
        EPWM_setCountModeAfterSync(base, EPWM_COUNT_MODE_DOWN_AFTER_SYNC);
        HRPWM_setRisingEdgeDelayLoadMode(ePWM[base], HRPWM_LOAD_ON_CNTR_ZERO_PERIOD);
        HRPWM_setFallingEdgeDelayLoadMode(ePWM[base], HRPWM_LOAD_ON_CNTR_ZERO_PERIOD);
        //-ve value indicates phase advance, +ve value indicates phase delay
        if(value < 0)
            epwmInfo[2].syncDirection = COUNT_UP_SYNC;
            value = -value;
        else
            epwmInfo[2].syncDirection = COUNT_DOWN_SYNC;
        uint32_t shift2Count = value/10;
        shift2Count <<= 8;
        if(value < 0)
            epwmInfo[3].syncDirection = COUNT_UP_SYNC;
            value = -value;
        else
            epwmInfo[3].syncDirection = COUNT_DOWN_SYNC;
        uint32_t shift3Count = value/10;
        shift3Count <<= 8;
        uint32_t oldPhase = epwmInfo[4].phaseShift>>8;
        if(value < 0)
            epwmInfo[4].syncDirection = COUNT_UP_SYNC;
            value = -value;
        else if(value >= 5000)
            value = EPWM_TIMER_TBPRD*10 - (value%(EPWM_TIMER_TBPRD*10));
        else
            epwmInfo[4].syncDirection = COUNT_DOWN_SYNC;
        uint32_t shift4Count = value/10;
        shift4Count <<= 8;
    //will update all final phase shift variables and step sizes
        uint16_t max_steps;
        int16_t pri_pw_diff = pri_pw - epwm_fw_state.curr_prim_pulse_ns;
        int16_t sec_pw_diff = sec_pw - epwm_fw_state.curr_sec_pulse_ns;
        int16_t phase_diff  = pri_sec_phase - epwm_fw_state.curr_phase_pri_sec_ns;
        if(pri_pw == EPWM_ZERO_PHASE_SHIFT && pri_sec_phase == EPWM_DEFAULT_PHASE_SHIFT
                                                        && sec_pw == EPWM_ZERO_PHASE_SHIFT)
            epwm_fw_state.pri_pulse_step = EPWM_ZERO_PHASE_SHIFT;
            epwm_fw_state.sec_pulse_step = EPWM_ZERO_PHASE_SHIFT;
            epwm_fw_state.phase_shift_step = EPWM_ZERO_PHASE_SHIFT;
        //finding the maximum phase, and calculating the max steps count
        else if(pri_pw_diff != EPWM_ZERO_PHASE_SHIFT && sec_pw_diff != EPWM_ZERO_PHASE_SHIFT
                                                        && phase_diff != EPWM_ZERO_PHASE_SHIFT)
            pri_pw_diff = (pri_pw_diff < 0) ? -pri_pw_diff : pri_pw_diff;
            sec_pw_diff = (sec_pw_diff < 0) ? -sec_pw_diff : sec_pw_diff;
            phase_diff = (phase_diff < 0) ? -phase_diff : phase_diff;
            if((pri_pw_diff >= sec_pw_diff) && (pri_pw_diff > phase_diff))
                max_steps = pri_pw_diff / EPWM_PHASE_SHIFT_STEP;
            else if((sec_pw_diff >= pri_pw_diff) && (sec_pw_diff > phase_diff))
                max_steps = sec_pw_diff / EPWM_PHASE_SHIFT_STEP;
            else
                max_steps = phase_diff / EPWM_PHASE_SHIFT_STEP;
            epwm_fw_state.pri_pulse_step = ((pri_pw_diff / max_steps) == 0 ? 1 : (pri_pw_diff / max_steps));
            epwm_fw_state.sec_pulse_step = ((sec_pw_diff / max_steps) == 0 ? 1 : (sec_pw_diff / max_steps));
            epwm_fw_state.phase_shift_step = ((phase_diff / max_steps) == 0 ? 1 : (phase_diff / max_steps));
        else
            //Don't do anything
                if (status == 2)
     Image showing PWM4A during phase transition from499 to 500.
    One more check I've done that, I've enabled PWM-ISR for DOWN_CMPB event. In the ISR I'm toggling one GPIO. I've found that, the ISR event is also not generated, when it's missing the pulse. I've attached image of scope. Yellow signal is EPWM4A(missing pulse), Green signal is GPIO Toggle on Down_CMPB event. I've attached drawn image of my understanding on the phase shift, correct me if I'm wrong. Kindly, verify and provide solution for this issue soon. Thanks
  • Hi Karthik,
    Glad you were able to review the threads and resolve the first part of the issue!
    Before we get into debugging this further, I again wanted to ask if you are using HR settings when testing (I know before, you said you weren't). It's always wise to test it without HR enabled to verify that it isn't just an HR configuration issueSlight smile.
    Your understanding looks correct to me. But I'm wondering if this again has to do with the timing of syncing and the specific value that may be generating the missing AQ. Does this missing AQ occur for all sync events when TBPHS = 500? Do you see the same behavior if you set your TBPHS to any other values? When exactly are you issuing the sync event to occur? And for system context - is there a reason why you need a phase shift of 500 in your application?
    Allison