Hello,
I am using TMS320F28388D as subordinate devices in an EtherCAT network that I intend to run at 4 kHz (250 us cycle time). I was originally intending to run the system with DC (Distributed Clock) enabled, but I found that the device seems to only support a minimum SYNC0 cycle time of 500 us. This is interpreting from the block below from ecat_def.h:
Blake,
1. Is it correct for me to conclude that this device does not support running with a 250 us DC cycle time? Can this be bypassed, or are there other C2000 devices that would support a 250 us cycle time with DC?
You can absolutely use a 250 us cycle time with DC. I have always configured this through the MainDevice, for example using TwinCAT. Since this value will be stored in the ESC registers, it is modifiable by either the C28X CPU or the MainDevice.
2. Is there a minimum supported cycle time when running without DC? The AL status code ALSTATUSCODE_CYCLETIMETOOSMALL does not seem to be used in my generated slave code so I'm not sure what PD cycle time limit would apply without DC.
I think the minimum cycle time is 1 us. Honestly the easiest way to check this would be to play with the settings in TwinCAT if you are able to use TwinCAT as your MainDevice.
Best Regards,
Ben Collier
Ben,
Thank you for your response. Question 2 is resolved and I was able to find the limit experimentally by playing with the settings as you suggested. With DC disabled I started seeing overrun errors below 40 microseconds with my network topology and application.
However, for question 1 I still have some confusion. You say that I can use a 250 us cycle time with DC, but as I said in the original message I already tried to use TwinCAT to set the task cycle time to 250 us and also set the SYNC0 cycle time to 250 us. When I do this and run on the TMS320F28388D subordinate devices I get the AL status code ALSTATUSCODE_DCSYNC0CYCLETIME and the subordinates do not progress past the Pre-op state. The value of the macro definition MIN_PD_CYCLE_TIME seems to suggest the minimum allowed SYNC0 cycle time is 500 us.
In order to bypass this error, in TwinCAT would I need to configure the SYNC0 cycle time to be an allowed value, like 500 us, while the task cycle time is 250 us? Otherwise, how do you recommend I configure the TwinCAT project to achieve the 250 us task cycle time with DC enabled?
Thank you,
Blake
Ben,
Thank you for your response. Question 2 is resolved and I was able to find the limit experimentally by playing with the settings as you suggested. With DC disabled I started seeing overrun errors below 40 microseconds with my network topology and application.
However, for question 1 I still have some confusion. You say that I can use a 250 us cycle time with DC, but as I said in the original message I already tried to use TwinCAT to set the task cycle time to 250 us and also set the SYNC0 cycle time to 250 us. When I do this and run on the TMS320F28388D subordinate devices I get the AL status code ALSTATUSCODE_DCSYNC0CYCLETIME and the subordinates do not progress past the Pre-op state. The value of the macro definition MIN_PD_CYCLE_TIME seems to suggest the minimum allowed SYNC0 cycle time is 500 us.
In order to bypass this error, in TwinCAT would I need to configure the SYNC0 cycle time to be an allowed value, like 500 us, while the task cycle time is 250 us? Otherwise, how do you recommend I configure the TwinCAT project to achieve the 250 us task cycle time with DC enabled?
Thank you,
Blake
Blake,
To clarify, I think that a task cycle time of 250us should be possible, but I am not sure about the SYNC0 cycle time.
In order to bypass this error, in TwinCAT would I need to configure the SYNC0 cycle time to be an allowed value, like 500 us, while the task cycle time is 250 us?
I think this is a good idea. Please check if your communication works with a higher SYNC0 cycle time while keeping the task cycle time at 250 us.
Best Regards,
Ben Collier