TMS320F28335: Trip Zone detection level

Prodigy 150 points

Replies: 1

Views: 22

Part Number: TMS320F28335

Dear Sir/Madam,

Trip zone at 28335 is negative edge triggered. I wonder what is the logic level of triggering? Could some sudden glitches cause trip zone interrupt to occur? Thanks a lot.

Mert Sahin

  • Mert,

    any signal that crosses below VIL, as specified in the data sheet, could cause the trip-zone to be triggered. For the one-shot latching mechanism to latch the signal we require the signal remain active for 3 cycles.

    Realistically extremely short pulses with be "gobbled" by the input buffer and not seen by the rest of the system, but this is not guaranteed.

    Datasheet link:https://www.ti.com/lit/gpn/tms320f28335 