Hi,
Im using DRV8912-Q1 to drive PDLC. when i active the half-bridge, it only on for 2 to 3 msec.
then i try to disable the Low-current open-load detection as page 51 in DS. it only disable the report and didnt disable the function.
This thread has been locked.
If you have a related question, please click the "Ask a related question" button in the top right corner. The newly created question will be automatically linked to this question.
Hi,
Im using DRV8912-Q1 to drive PDLC. when i active the half-bridge, it only on for 2 to 3 msec.
then i try to disable the Low-current open-load detection as page 51 in DS. it only disable the report and didnt disable the function.
Hello,
We will investigate your question and get back to you within 24-48 hours.
Regards,
Pablo Armet
Hello,
It looks like if you set the OLD_OP bit in the OLD_CTRL_2 register to 1, then OUTX pins stay in their previous state and do not react to the OLD fault unless the user takes action. Similarly, the OLD_REP bit determines if the OLD fault will report on the nFAULT pin or only in the IC_STAT register. Table 8 summarizes the open-load detection feature and conditions. The OLD control registers (OLD_CTRL_1 and OLD_CTRL_2) allow the user to disable OLD on the OUTX pins with the HBX_OLD_DIS bits
Look through pages 46 and 47 in the datasheet and see if that works for you.
Regards,
Jacob T.