We have several similar designs using a UCD9240 in a system driving either three or four PTD08A006W to provide multiple (single phase) rails. These rails are relatively low-current (considerably below rating), and we only use the PTDs for design expediency. After some issues (many of which can be found in this forum) we have gotten all of them operational past the testing stage, but we are now having considerable reliability issues.

The first issue we had was regarding very repeatable temperature related failures (see separate thread). We managed to solve this by trimming the main supply voltage to ~5.3V instead of the 5V we had designed for (these modules were supposed to work down to 4.5V or so).

After some time testing on a very similar system that runs at lower temperatures and needs tighter constraints on the 5V main supply (10 separate units), we started noticing power-up failures. In which at least one of the rails would not come up consistently (failing more than 60% of the time, much more in one case), this meant that theUCD9240 will not reach 'power-good' state, and would leave a subset of rails powered-up. Given the previous issue, we decided to trim the 5V supply upwards (to 5.15V). This reduced the recurrence of the problem, but we still see random failures (approaching 1%) on power-up.

In all cases the logged failures are either (1) a rail fault line (input over-current), or (2) a large (impossible) negative current transient on a module. Where a fault line assertion is the most common of the two.

We have also increased the gap between operation Vin thresholds, verified all transients around the modules during power-up, increased power-up delays, reduced power-up slopes, raised the 5V supply, and we see no cause for these fault conditions. Our rail dependencies are rather conservative, as one rail coming down only brings subsequent rails down Our boards are 12-layer, with separate power and analog ground planes (one-point) connection, with far more bypassing and filtering than what is minimally required (it is a very low-noise system).

Now we are starting to see random power faults during operation of these same systems (only one of the 10 so far, but that is how most of the other issues have started). I would like to know:

  1. Can the PTD08A006W / UCD9240 combination be reliably used on a 5V system? (all reference designs that I have seen use 12V)
  2. Would an UCD9248 (or 9244 if it is available) work better under these conditions?

Thanks