Hi all,
currently we have some challanges/ questions about the EtherCAT Error Counters.
If multiple devices are connected in a line topologie and one of the slaves are put into INIT system State of EtherCAT the counter seems to be incrementing once.
The counters are also randomly incrementing from time to time while one of the devices is still in INIT state.
The counters I am talking about are described here on page 15 https://www.ethercat.org/download/documents/ethercat_diagnosis_for_users.pdf
We tracked those counters down to be implemented in the PRU firmware.
I also had contact with the ETG which confirmed that changing the system state of a EtherCAT slave should not have any incluence on that counters.
Is this a known issue of the current implementation of the PRU firmware?
Can TI reproduce this with the reference implementation on the Evaluation Boards?
Thanks
Fabian
Hi Fabian,
May I know which SDK version are you using for this multiple SubDevice testing?
Regards,
Aaron
Hi Aaron,
sure, we are currently using the Industrial Coms SDK Version 09.02.00
Regards
Fabian
The counters are also randomly incrementing from time to time while one of the devices is still in INIT state.
Which specific counters are incremented? Is there a wireshark log?
the RX Error Counters. See from above in more detail the Frame Error (Register 0x0300 and 0x0302) Counters. I can try to produce a whireshark today and send it over. May we then switch to E-Mails?
Hi Fabian,
So I tried the EtherCAT Beckhoff Demo from Industrial Coms SDK Version 09.02.00.15 and connected 2 SubDevices in line topology to TwinCAT. I tested with Free Run mode as well as DC Synchronization mode (at cycle time of 50us) and I don't see the Error registers (0x0300 : 0x0303) getting incremented when I take one of the SubDevice to INIT, keeping the MainDevice and the other SubDevice in OP state.
Attaching the wireshark logs for the same: EtherCAT_09_02_00_15_MultiDevice_Test_50us.zip
Do let me know if I'm missing on anything for reproduction of the issue.
Regards.
Aaron
Hi Aaron, we will also create some wireshark logs on our side and will provide them.
Thanks for the clarification already!
Hi Aaron, can you do the same test with 3 subdevices and put the middle one into INIT?
Thanks!
Hi Aaron,
Here is the log of Wireshark.
EtherCat_Wireshark_RxError_Counter.zip
We have configured 3 IO-link master in Line topology. Also, to observer the behaviour we used following ST code to read out RxError.
etcreadmemory1(xExecute := xRead, usiCom:=1, wSlaveAddress := .BNI_XG5_538_1B5_Z067.PhysSlaveAddr, xAutoIncAdr := FALSE, xBroadcast := FALSE, uiMemOffset := 16#0310, iSize := 2, pDest := ADR(LinkError1), udiTimeout := 500); etcreadmemory2(xExecute := xRead, usiCom:=1, wSlaveAddress := .BNI_XG5_538_1B5_Z067.PhysSlaveAddr, xAutoIncAdr := FALSE, xBroadcast := FALSE, uiMemOffset := 16#0300, iSize := 4, pDest := ADR(RxError1), udiTimeout := 500); etcreadmemory3(xExecute := xRead, usiCom:=1, wSlaveAddress := .BNI_XG5_538_1B5_Z067_1.PhysSlaveAddr, xAutoIncAdr := FALSE, xBroadcast := FALSE, uiMemOffset := 16#0310, iSize := 2, pDest := ADR(LinkError2), udiTimeout := 500); etcreadmemory4(xExecute := xRead, usiCom:=1, wSlaveAddress := .BNI_XG5_538_1B5_Z067_1.PhysSlaveAddr, xAutoIncAdr := FALSE, xBroadcast := FALSE, uiMemOffset := 16#0300, iSize := 4, pDest := ADR(RxError2), udiTimeout := 500); etcreadmemory5(xExecute := xRead, usiCom:=1, wSlaveAddress := .BNI_ECT_508_105_Z067.PhysSlaveAddr, xAutoIncAdr := FALSE, xBroadcast := FALSE, uiMemOffset := 16#0310, iSize := 2, pDest := ADR(LinkError3), udiTimeout := 500); etcreadmemory6(xExecute := xRead, usiCom:=1, wSlaveAddress := .BNI_ECT_508_105_Z067.PhysSlaveAddr, xAutoIncAdr := FALSE, xBroadcast := FALSE, uiMemOffset := 16#0300, iSize := 4, pDest := ADR(RxError3), udiTimeout := 500);
and the result is following:
I hope it will help you to reproduce the issue.
Best regards,
Shahin
Hi Shahin,
To clarify myself, which example are you using for this?
Regards,
Aaron
Hi Aaron,
we are not using any TI examples but our own implementation but using Sitara AM24 Processor and the PRU FW from SDK 9.02.
Best Regards
Fabian
Hi Fabian,
From the logs, looks like 0x302 ESC Register is getting incremented. And from the register description, this error counter gets incremented when RX Error is detected.
Recommend to check the HW or PHY for any noise factor which can affect the EtherCAT communication.
Regards,
Aaron
Hi Aaron, we grounded our modules accordlingly. The last module is a older revision IO-Link master (with another vendors processor) which is in the same line and does not show this behavoir. We only see it with the sitara based IO-Link Gateways.
Can you reproduce it with 3 devices?
Hi Fabian,
Can you monitor RX_ERR pin from the PHY during the tests or monitor RX_ERR counter register of the PHY (0x15 offset in TI PHYs).
Can you reproduce it with 3 devices?
Regards,
Aaron
Hi Fabian,
Hi Aaron, can you do the same test with 3 subdevices and put the middle one into INIT?
Regards,
Aaron
Hi Aaron,
here I attached complete Wireshark log.
For the above, can you provide the FMMU configurations and the complete wireshark logs for EtherCAT communication (from INIT to OP and till the error counter increment is observed) ?
EtherCat_Wireshark_RxError_Counter_2.zip
Best regards
Shahin
Thank you Shahin for the logs. I’ll try to reproduce with this.
Can you monitor RX_ERR pin from the PHY during the tests or monitor RX_ERR counter register of the PHY (0x15 offset in TI PHYs).
Regards,
Aaron
Hi Aaron,
thanks!
We will try to set something up where we monitor RX_ERR.
Do you think a call we help where we show you the issue?
Regards,
Fabian
Hi Fabian,
Do you think a call we help where we show you the issue?
Meanwhile, can you also share the value in ESC registers? I’m referring to the values in the memory space 0x30090000 to 0x30090ECF.
Regards,
Aaron
Hi Fabian, Shahin,
Following the FMMU configurations from the logs you shared, we created a reproduction environment with the following topology:
PC <-> ET2000 <-> AM243x-LP (SD1) <-> AM243x-LP (SD2) <-> AM243x-LP (SD3)
SD1:
InputSize - 32 bytes
OutputSize - 2 bytes
SD2:
InputSize - 32 bytes
OutputSize - 2 bytes
SD3:
InputSize - 16 bytes
OutputSize - 0 bytes
After doing a playback of the packets (EtherCat_Wireshark_RxError_Counter_2), I'm not seeing the RX Error Counter registers getting incremented when SD2 is taken to INIT.
Attaching the logs for the same: Baluff_3_Device_Issue_Reproduction_Playback.pcapng
We will try to set something up where we monitor RX_ERR.
Regards,
Aaron
Hi Aaron,
Can you monitor RX_ERR pin from the PHY during the tests or monitor RX_ERR counter register of the PHY (0x15 offset in TI PHYs).
Meanwhile, can you also share the value in ESC registers? I’m referring to the values in the memory space 0x30090000 to 0x30090ECF.
I have attached the memory value here ESC_registers_0x30090000_0x30090ECF.zip.
Thank you so much
Best regards
Shahin
Hi Shahin,
The counter value was 0, when we stop the program read the counter value. However, when place a breakpoint inside MDIO_phyRegRead method we notice some value in RX_ERR counter.
I have attached the memory value here ESC_registers_0x30090000_0x30090ECF.zip.
Regards,
Aaron
Hi Aaron,
Is this the case all the time, that is, each time the break point is hit, RX_ERR counter is incremented? Recommend you to log the counter value in the terminal/console for proper monitoring so that it aligns with the RX_ERR pin reading
Yes, it was. I will try your suggested method again and let you know the outcome.
Unfortunately, this week I'm not the at office anymore. I will provide this data to you next week
Regards
Shahin
Hi Shahin,
Unfortunately, this week I'm at office anymore. I provide this day to you next week
Yeah sure no problem.
Regards,
Aaron
Hi Aaron,
Is this the case all the time, that is, each time the break point is hit, RX_ERR counter is incremented? Recommend you to log the counter value in the terminal/console for proper monitoring so that it aligns with the RX_ERR pin reading.
The console output shows counter value 0, However in Codesys there are non-zero values.
And here is the memory register value save as TI data, 1526.ESC_registers_0x30090000_0x30090ECF.zip
The memory register value is saved from the 2nd node.
Best regards
Shahin
Hi Shahin,
The console output shows counter value 0, However in Codesys there are non-zero values.
And here is the memory register value save as TI data, 1526.ESC_registers_0x30090000_0x30090ECF.zip
Also could you provide the values in the following register spaces:
Regards,
Aaron
Hi Aaron,
The values doesn't look right. I don't see the EtherCAT Firmware version in the first 4 bytes and overall it looks different than the expected values. Are you using ICSSG0 or ICSSG1 instance for EtherCAT implementation?
We are using ICSSG1 instance.
Followed by choosing System_View as Memory Page in the next window
In my Code Composer studio System_View option is missing
0x30090000 - 0x30090ECF (for ICSSG1)
ESC_registers_0x30090000_0x30090ECF.dat
0x300B2000 to 0x300B206C (for ICSSG1)
ESC_registers_0x300B2000_0x300B206C.dat
0x300B2400 to 0x300B2484 (for ICSSG1)
ESC_registers_0x300B2400_0x300B2484.dat
Regards
Shahin
Thank you Shahin for the memory dump.
Looking at the MII_RT Registers, I see that bit2 of MII_RT_RX_ERR0 is set:
As mentioned in the description, this points to the fact that frame total byte count is less than the defined value. This looks like the MainDevice is not transmitting as expected?
Additionally, is it possible to test with a different MainDevice? And is it possible to use a tap to capture the EtherCAT communication - like ET2000 | Industrial Ethernet multi-channel probe. Since Reg 0x0302 is getting incremented, it corresponds to the reverse path (Rx at port1). So a tap can be kept in between and see if CRC is generated and if yes, which device is causing the issue.
Regards,
Aaron
Hi Aaron,
Thank you for pointing out the possible issue.
Additionally, is it possible to test with a different MainDevice?
Sure, I will try to reproduce the issue with Backhoff PLC and I will share the result with you.
As mentioned in the description, this points to the fact that frame total byte count is less than the defined value. This looks like the MainDevice is not transmitting as expected?
In the meantime, could you also tell me where these memory description can be found, so that I can go through it and understand stand the context too?
And is it possible to use a tap to capture the EtherCAT communication
I will search it in my team if they have one, then I will use and check with it. I will give you the feedback.
Best regards
Shahin
Hi Shahin,
In the meantime, could you also tell me where these memory description can be found, so that I can go through it and understand stand the context too?
I will search it in my team if they have one, then I will use and check with it. I will give you the feedback.
Regards,
Aaron