Tool/software:
Hi Champ,
I am asking for my customer.
In general, OCP and OVP protection are normally using CMPSS to detect for implementation, then if the event occurs, signal is connected to the ePWM X-BAR for ePWM trip response.
Checking on the total response time from CMPSS detection to EPWM trip taking action for OCP/OVP protection.
(1). Is it step response time (21~60ns) for CMPSS Response time parameter + td(TZ-PWM) + the parasitic load on the EPWM pin ? Any parameter missing here ?
(2). From customer's observation of testing the OCP on their own board, it takes about 20ms which ns should be a reasonable timing at here. What could be the possible issues here ?
CH1: PWM output ; CH2: OCP PIN trigger signal
Thanks and regards,
Johnny
Hi Johnny,
What frequency is the customer running their device clock at, specifically the EPWM clock? 20 ms is much too long response time for OCP/OVP if they are utilizing the CMPSS + EPWM trip zone.
For fastest response, CTRIPH/CTRIPL should be configured to come from the asynchronous input. The only other source of delay is coming from the EPWM which has 3 TBCLK cycle latch time to register trip signal from CMPSS. If TBCLK is configured as divided from the device SYSCLK, this can lead to elongation of trip timinig.
Regards,
Peter