Other Parts Discussed in Thread: AMC1303E2510, AMC1306M25
I'm using Filters1, 2 and 3 of the TMS320F28075 SDFM1 to read the Manchester Encoded output from 3 separate AMC1303E2510 chips. The AMC1303E2510 has it's own internally generated 10MHz CLK, therefore I'm using CMPC and CMPD of ePWM11 to synchronise filters1, 2 and 3 of SDFM1. After the result from each Filter is read, it is re-scaled to the DAC range (0-4095) and the 3 filter outputs are output on the 3 DACs. I've attached the main .c file of the project below.
The problem I have is that the output from the SDFM module is wrong sometimes. In the oscilloscope shot below:
- CH1 (yellow) is a +/-10V input (via resistor divider) to the AMC1303 chip for Filter 1. +/-10V produces +/-250mV at the AMC1303 input.
- CH2 (pink) is the DAC output for Filter 1 (note that it is passed through an external op-amp buffer to increase it's amplitude).
You can see in the zoom in of CH2 that the DAC output is wrong for approx. 40us (in the code the SDFM sampling period is approx. 20us so this corresponds to 2 incorrect values from the SDFM module). I have also verified that the problem is not with the conversion to the DAC (i.e. the raw data read from the SDDATA register for filter 1 is incorrect).
The ISR routine, epwm1_isr, is triggered when ePWM1 counter is 0. It is configured in UP COUNT mode. The PWM period is set to 4 times the SDFM sampling period. This is because after a PWM sync, the first two SDFM output values are incorrect (with a SINC3 filter). ePWM11 is setup the same as ePWM1 and is synced to the ePWM1 counter by the synchronisation pulse input from ePWM1 fed through ePWM10.
ePWM11.CMPC and CMPD are set to SDFM_RESET_CMP_VALUE. SDFM_RESET_CMP_VALUE is set so that it occurs Latency of data filter + 5 SD clock cycles before the PWM counter resets to 0. Therefore after the CMPC/CMPD PWM sync there should be time for 3 SDFM output values before the ISR triggers. Therefore I'm confident that the problem is not because I am reading one of the 2 incorrect samples after a PWMSYNC event.
In the ISR the ACK and the Modulator failure flags for filters 1, 2 and 3 are checked. If any of the ACK flags are NOT set or if any of the modulator failure flags are set, then the routine pauses (using ESTOP0). However this never happens, even when there is an incorrect value.
Finally, I have seen in the datasheet and other threads that the delta-sigma chip (AMC1303E2510 in this case) CLK period must be between 8*T_SYSCLK - 20*T_SYSCLK. In my code I am using the line
InitSysPll(INT_OSC2,IMULT_10,FMULT_0,PLLCLK_BY_1);
to set the MCU CLK frequency to 100MHz. Therefore T_SYSCLK = 10ns. So the delta-sigma CLK period must be between 80ns - 200ns. For a 10MHz delta-sigma CLK, the period is 100ns so that should be fine.
Do you see anything wrong with the setup I have described? Have you seen this kind of behaviour before?
Many thanks,
Fearghal
//########################################################################### // // FILE: sdfm_pwm_sync_cpu_cpu01.c // // TITLE: SDFM PWM sync Example for F2807x. // //! \addtogroup cpu01_example_list //! <h1> SDFM PWM Sync </h1> //! //! In this example, SDFM filter data is read by CPU in SDFM ISR routine. The //! SDFM configuration is shown below: //! - SDFM1 is used in this example //! - MODE2 Input control mode selected //! - Comparator settings //! - Sinc3 filter selected //! - OSR = 32 //! - HLT = 0x7FFF (Higher threshold setting) //! - LLT = 0x0000(Lower threshold setting) //! - Data filter settings //! - 3 filter modules enabled //! - Sinc3 filter selected //! - OSR = 50 //! - All the 3 filters are synchronized by using PWMSYNC //! - Filter output represented in 16 bit format //! - In order to convert 25 bit Data filter //! into 16 bit format user needs to right shift by 2 bits for //! Sinc3 filter with OSR = 50 //! - Interrupt module settings for SDFM filter //! - All the 4 higher threshold comparator interrupts disabled //! - All the 4 lower threshold comparator interrupts disabled //! - All the 4 modulator failure interrupts disabled //! - All the 4 filters will NOT generate an interrupt when a new filter data //! is available //! - The interrupt is controlled by ePWM1 //! // //########################################################################### // $TI Release: F2807x Support Library v3.05.00.00 $ // $Release Date: Tue Jun 26 03:19:11 CDT 2018 $ // $Copyright: // Copyright (C) 2014-2018 Texas Instruments Incorporated - http://www.ti.com/ // // Redistribution and use in source and binary forms, with or without // modification, are permitted provided that the following conditions // are met: // // Redistributions of source code must retain the above copyright // notice, this list of conditions and the following disclaimer. // // Redistributions in binary form must reproduce the above copyright // notice, this list of conditions and the following disclaimer in the // documentation and/or other materials provided with the // distribution. // // Neither the name of Texas Instruments Incorporated nor the names of // its contributors may be used to endorse or promote products derived // from this software without specific prior written permission. // // THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS // "AS IS" AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT // LIMITED TO, THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS FOR // A PARTICULAR PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE COPYRIGHT // OWNER OR CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT, INCIDENTAL, // SPECIAL, EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING, BUT NOT // LIMITED TO, PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES; LOSS OF USE, // DATA, OR PROFITS; OR BUSINESS INTERRUPTION) HOWEVER CAUSED AND ON ANY // THEORY OF LIABILITY, WHETHER IN CONTRACT, STRICT LIABILITY, OR TORT // (INCLUDING NEGLIGENCE OR OTHERWISE) ARISING IN ANY WAY OUT OF THE USE // OF THIS SOFTWARE, EVEN IF ADVISED OF THE POSSIBILITY OF SUCH DAMAGE. // $ //########################################################################### // // Included Files // #include "F28x_Project.h" #include "F2807x_struct.h" #include "F2807x_sdfm_drivers.h" /* Device Related Defines */ #define CPU_SYS_CLOCK (100*1000000) #define PWMSYSCLOCK_FREQ (50*1000000) #define ECAPSYSCLOCK_FREQ (100*1000000) // // User Defines // #define SDFM_MODE MODE_2 #define SDFM_FILTER_TYPE SINC3 #define SDFM_OSR OSR_50 // Value is for OSR_50 is actually 49 #define SDFM_NUM_BITS_RIGHT_SHIFT SHIFT_2_BITS // This setting depends on the OSR and filter type. See datasheet for details #define SDFM_SCALE_FACTOR 0.00001525878906 // = ( 0.5 / 32768.0 ). This assumes that the SDFM output is from -32768 to 32767 (i.e. int16_t) #if SDFM_FILTER_TYPE == SINCFAST #define NUM_INCORRECT_SAMPLES_AFTER_SYNC 2 #elif SDFM_FILTER_TYPE == SINC1 #define NUM_INCORRECT_SAMPLES_AFTER_SYNC 0 #elif SDFM_FILTER_TYPE == SINC2 #define NUM_INCORRECT_SAMPLES_AFTER_SYNC 1 #elif SDFM_FILTER_TYPE == SINC3 #define NUM_INCORRECT_SAMPLES_AFTER_SYNC 2 #endif #define SDCLK_FREQ ( 0.96 * 10000000.0 ) // delta-sigma device dependent if the chip uses it's own internal CLK. Use lowest possible frequency #define SD_OUTPUT_FREQ ( SDCLK_FREQ / (float)(SDFM_OSR + 1) ) #define PWM_CLK_IN_SDFM_CLK ( PWMSYSCLOCK_FREQ / SDCLK_FREQ ) #define PWM_CLK_IN_SDFM_OSR ( PWMSYSCLOCK_FREQ / SD_OUTPUT_FREQ ) // Define the filter latencies. Add 5 SD CLK cycles as per datasheet. // Use 0.96*SDCLK_FREQ to account for 4% tolerance on the internal CLK frequency // of the AMC1303 #define SDFM2_LATENCY_PWM_CLK_COUNT ( ( (NUM_INCORRECT_SAMPLES_AFTER_SYNC + 1) * PWM_CLK_IN_SDFM_OSR ) + ( 5.0 * PWM_CLK_IN_SDFM_CLK ) ) #define EPWM_TIMER_PERIOD ( (NUM_INCORRECT_SAMPLES_AFTER_SYNC + 2) * PWM_CLK_IN_SDFM_OSR ) #define SDFM_RESET_CMP_VALUE ( EPWM_TIMER_PERIOD - SDFM2_LATENCY_PWM_CLK_COUNT ) // // SDFM Defines // #define SDFM_PIN_MUX_OPTION1 1 #define SDFM_PIN_MUX_OPTION2 2 #define SDFM_PIN_MUX_OPTION3 3 // // DAC Defines // #define REFERENCE_VDAC 0 #define REFERENCE_VREF 1 #define DACA 1 #define DACB 2 #define DACC 3 #define DAC_REFERENCE_VOLTAGE REFERENCE_VREF // // ePWM Defines // #define EPWM1_TIMER_TBPRD EPWM_TIMER_PERIOD // Period register #define EPWM10_TIMER_TBPRD EPWM_TIMER_PERIOD // Period register #define EPWM11_TIMER_TBPRD EPWM_TIMER_PERIOD // Period register #define EPWM11_CMPC SDFM_RESET_CMP_VALUE #define EPWM11_CMPD SDFM_RESET_CMP_VALUE #define EPWM12_TIMER_TBPRD EPWM_TIMER_PERIOD // Period register #define EPWM12_CMPC SDFM_RESET_CMP_VALUE #define EPWM12_CMPD SDFM_RESET_CMP_VALUE #define EPWM_CMP_UP 1 #define EPWM_CMP_DOWN 0 // // Globals // uint16_t gPeripheralNumber, gPWM_number = 12; int16_t Filter1_Result = 0; int16_t Filter2_Result = 0; int16_t Filter3_Result = 0; int16_t Filter4_Result = 0; uint16_t SDFMReadingCounter = 0; uint32_t sdfmReadFlagRegister; #pragma DATA_SECTION(Filter1_Result,"Filter1_RegsFile"); #pragma DATA_SECTION(Filter2_Result,"Filter2_RegsFile"); #pragma DATA_SECTION(Filter3_Result,"Filter3_RegsFile"); #pragma DATA_SECTION(Filter4_Result,"Filter4_RegsFile"); volatile struct DAC_REGS* DAC_PTR[4] = {0x0,&DacaRegs,&DacbRegs,&DaccRegs}; // // Function Prototypes // void Sdfm_configurePins(uint16_t); void InitEPwm(void); void done(void); void GPIO_configureDiagnosticPins(void); void GPIO_setOutputValue(uint32_t GPIONumber, uint32_t outputValue); void GPIO_setOutputValue43(uint32_t GPIONumber, uint32_t outputValue); void configureDAC(Uint16 dac_num); __interrupt void Sdfm2_ISR(void); void InitEPwm1Example(void); void InitEPwm10Example(void); void InitEPwm11Example(void); void InitEPwm12Example(void); __interrupt void epwm1_isr(void); // Debug variables #define MEMORY_SIZE 16 uint32_t SDFM_ISR_counter = 0; int16_t Filter2_Result_Memory[MEMORY_SIZE]; int16_t Filter3_Result_Memory[MEMORY_SIZE]; uint16_t memory_pointer = 0; int32_t debug_1 = EPWM1_TIMER_TBPRD; int32_t debug_2 = SDFM_RESET_CMP_VALUE; uint32_t CH1_ACTIVE; uint32_t CH2_ACTIVE; uint32_t CH3_ACTIVE; uint32_t FAULT; // // Main // void main(void) { uint16_t pinMuxoption; uint16_t HLT, LLT; // // Initialize System Control: // PLL, WatchDog, enable Peripheral Clocks // This example function is found in the F2807x_SysCtrl.c file. // InitSysCtrl(); // // Clear all __interrupts and initialize PIE vector table: // Disable CPU __interrupts // DINT; // // Initialize PIE control registers to their default state. // The default state is all PIE __interrupts disabled and flags // are cleared. // This function is found in the F2807x_PieCtrl.c file. // InitPieCtrl(); // // Disable CPU __interrupts and clear all CPU __interrupt flags: // IER = 0x0000; IFR = 0x0000; // // Initialize the PIE vector table with pointers to the shell Interrupt // Service Routines (ISR). // This will populate the entire table, even if the __interrupt // is not used in this example. This is useful for debug purposes. // The shell ISR routines are found in F2807x_SysCtrl.c. // This function is found in F2807x_SysCtrl.c. // InitPieVectTable(); // // Interrupts that are used in this example are re-mapped to // ISR functions found within this file. // EALLOW; PieVectTable.EPWM1_INT = &epwm1_isr; PieVectTable.SD2_INT = &Sdfm2_ISR; EDIS; // // For this example, only initialize the ePWM // EALLOW; CpuSysRegs.PCLKCR0.bit.TBCLKSYNC = 0; EDIS; InitEPwm1Example(); InitEPwm10Example(); InitEPwm11Example(); InitEPwm12Example(); EALLOW; CpuSysRegs.PCLKCR0.bit.TBCLKSYNC = 1; EDIS; // // Configure DACA and DACB // configureDAC(DACA); configureDAC(DACB); configureDAC(DACC); #ifdef CPU1 pinMuxoption = SDFM_PIN_MUX_OPTION1; // // Configure GPIO pins as SDFM pins // Sdfm_configurePins(pinMuxoption); #endif // // Select SDFM1 // gPeripheralNumber = SDFM1; // // Input Control Module // // Configure Input Control Mode: Modulator Clock rate = Modulator data rate // Sdfm_configureInputCtrl(gPeripheralNumber, FILTER1, SDFM_MODE); Sdfm_configureInputCtrl(gPeripheralNumber, FILTER2, SDFM_MODE); Sdfm_configureInputCtrl(gPeripheralNumber, FILTER3, SDFM_MODE); Sdfm_configureInputCtrl(gPeripheralNumber, FILTER4, SDFM_MODE); // // Comparator Module // HLT = 0x7FFF; //Over value threshold settings LLT = 0x0000; //Under value threshold settings // // Configure Comparator module's comparator filter type and comparator's OSR // value, higher threshold, lower threshold // Sdfm_configureComparator(gPeripheralNumber, FILTER1, SINC3, OSR_32, HLT, LLT); Sdfm_configureComparator(gPeripheralNumber, FILTER2, SINC3, OSR_32, HLT, LLT); Sdfm_configureComparator(gPeripheralNumber, FILTER3, SINC3, OSR_32, HLT, LLT); Sdfm_configureComparator(gPeripheralNumber, FILTER4, SINC3, OSR_32, HLT, LLT); // // Enable Master filter bit: Unless this bit is set none of the filter modules // can be enabled. All the filter modules are synchronized when master filter // bit is enabled after individual filter modules are enabled. All the filter // modules are asynchronized when master filter bit is enabled before // individual filter modules are enabled. // Sdfm_enableMFE(gPeripheralNumber); // // Data filter Module // // Configure Data filter modules filter type, OSR value and // enable / disable data filter // If the OSR/Filter type combination have an output range that is 16-bit or less, // then there is no need to right shift bits. However be careful with this. Sdfm_configureData_filter(gPeripheralNumber, FILTER1, FILTER_ENABLE, SDFM_FILTER_TYPE, SDFM_OSR, DATA_16_BIT, SDFM_NUM_BITS_RIGHT_SHIFT); Sdfm_configureData_filter(gPeripheralNumber, FILTER2, FILTER_ENABLE, SDFM_FILTER_TYPE, SDFM_OSR, DATA_16_BIT, SDFM_NUM_BITS_RIGHT_SHIFT); Sdfm_configureData_filter(gPeripheralNumber, FILTER3, FILTER_ENABLE, SDFM_FILTER_TYPE, SDFM_OSR, DATA_16_BIT, SDFM_NUM_BITS_RIGHT_SHIFT); Sdfm_configureData_filter(gPeripheralNumber, FILTER4, FILTER_ENABLE, SDFM_FILTER_TYPE, SDFM_OSR, DATA_16_BIT, SDFM_NUM_BITS_RIGHT_SHIFT); // // PWM11.CMPC, PWM11.CMPD, PWM12.CMPC and PWM12.CMPD signals cannot synchronize // the filters. This option is not being used in this example. // EDIT: they can synchronise the filters and are being used Sdfm_configureExternalreset(gPeripheralNumber,FILTER_1_EXT_RESET_ENABLE, FILTER_2_EXT_RESET_ENABLE, FILTER_3_EXT_RESET_ENABLE, FILTER_4_EXT_RESET_ENABLE); // // Enable interrupts // // Following SDFM interrupts can be enabled / disabled using this function. // Enable / disable comparator high threshold // Enable / disable comparator low threshold // Enable / disable modulator clock failure // Enable / disable filter acknowledge // Sdfm_configureInterrupt(gPeripheralNumber, FILTER1, IEH_DISABLE, IEL_DISABLE, MFIE_ENABLE, AE_ENABLE); Sdfm_configureInterrupt(gPeripheralNumber, FILTER2, IEH_DISABLE, IEL_DISABLE, MFIE_ENABLE, AE_ENABLE); Sdfm_configureInterrupt(gPeripheralNumber, FILTER3, IEH_DISABLE, IEL_DISABLE, MFIE_ENABLE, AE_ENABLE); Sdfm_configureInterrupt(gPeripheralNumber, FILTER4, IEH_DISABLE, IEL_DISABLE, MFIE_DISABLE, AE_DISABLE); // Setup Diagnostic GPIO output pins GPIO_configureDiagnosticPins(); // // Enable SDFM master interrupt // Sdfm_enableMIE(gPeripheralNumber); // The interrupt triggers on counter = 0. Wait until just after we've passed zero and then // enable the ePWM interrupt. By doing this there should be a valid SDFM output value waiting // for the first interrupt while( ( (*EPWM[gPWM_number]).TBCTR < 10 ) || ( (*EPWM[gPWM_number]).TBCTR > 100 ) ); // // Enable CPU INT3 which is connected to ePWM INT // IER |= M_INT3; // // Enable EPWM INTn in the PIE: Group 3 interrupt 1-3 // PieCtrlRegs.PIEIER3.bit.INTx1 = 1; // Enable ePWM Interrupt EALLOW; EPwm1Regs.ETSEL.bit.INTEN = 1; // Enable INT EDIS; // Enable global interrupt bit EINT; while(1); } // // ePWM1 ISR __interrupt void epwm1_isr(void) { // Increment ISR counter SDFM_ISR_counter++; // Filter 1 is bit0, filter 4 is bit3 // filters 1, 2 and 3 are active uint32_t SDFM_modulator_failure_mask = 0x0700; uint32_t SDFM_SD1_ACK_mask = 0x1000; uint32_t SDFM_SD2_ACK_mask = 0x2000; uint32_t SDFM_SD3_ACK_mask = 0x4000; // // Read SDFM flag register (SDIFLG) // sdfmReadFlagRegister = Sdfm_readFlagRegister(gPeripheralNumber); // Turn ON uP_CHX_ACTIVE_LED for each channel that is active CH1_ACTIVE = (sdfmReadFlagRegister & SDFM_SD1_ACK_mask) >> 12; CH2_ACTIVE = (sdfmReadFlagRegister & SDFM_SD2_ACK_mask) >> 13; CH3_ACTIVE = (sdfmReadFlagRegister & SDFM_SD3_ACK_mask) >> 14; // Turn ON uP_FAULT_LED if any of the Modulator Failure Flags are set FAULT = (sdfmReadFlagRegister & SDFM_modulator_failure_mask); // // Read each SDFM filter output and store it in respective filter // result array // Filter1_Result = SDFM1_READ_FILTER1_DATA_16BIT; Filter2_Result = SDFM1_READ_FILTER2_DATA_16BIT; Filter3_Result = SDFM1_READ_FILTER3_DATA_16BIT; // // Write the current SDFM value to buffered DAC // DACA and DACB were swapped to make layout routing easier // DACA = uP_ANALOG_D2 // DACB = uP_ANALOG_D1 // DACC = uP_ANALOG_D3 DAC_PTR[DACA]->DACVALS.all = ((Filter2_Result * SDFM_SCALE_FACTOR) + 0.5) * 4095; DAC_PTR[DACB]->DACVALS.all = ((Filter1_Result * SDFM_SCALE_FACTOR) + 0.5) * 4095; DAC_PTR[DACC]->DACVALS.all = ((Filter3_Result * SDFM_SCALE_FACTOR) + 0.5) * 4095; // If any Filter ACK flag is NOT set, or if any Modulator Failure Flag is set, stop execution if ( !CH1_ACTIVE || !CH2_ACTIVE || !CH2_ACTIVE || (FAULT > 0) ) { // Debug ESTOP0; } // // Clear SDFM flag register // Sdfm_clearFlagRegister(gPeripheralNumber, sdfmReadFlagRegister); // // Clear INT flag for this timer // EPwm1Regs.ETCLR.bit.INT = 1; // // Acknowledge this interrupt to receive more interrupts from group 3 // PieCtrlRegs.PIEACK.all = PIEACK_GROUP3; } // // Sdfm2_ISR - SDFM 2 ISR // __interrupt void Sdfm2_ISR(void) { // Turn ON LED to show that ISR is active GPIO_setOutputValue(41, 1); // Increment ISR counter SDFM_ISR_counter++; uint32_t SDFM_active_filter_mask = 0x6; // Check if this interrupt was triggered by a Moudulator Failure Flag if ( (Sdfm_readFlagRegister(gPeripheralNumber) >> 8) & SDFM_active_filter_mask) { // Debug ESTOP0; } // Filters 2 and 3 are active. Wait until there is new data available for both. // Use mask to select which filters to wait for. while ( ( (Sdfm_readFlagRegister(gPeripheralNumber) >> 12) & SDFM_active_filter_mask) != SDFM_active_filter_mask ) { // just wait // ESTOP0; } // We need to ignore the first few filter output values after a sync. SDFMReadingCounter++; // // Read each SDFM filter output and store it in respective filter // result array // Filter1_Result = SDFM2_READ_FILTER1_DATA_16BIT; Filter2_Result = SDFM2_READ_FILTER2_DATA_16BIT; Filter3_Result = SDFM2_READ_FILTER3_DATA_16BIT; Filter4_Result = SDFM2_READ_FILTER4_DATA_16BIT; Filter2_Result_Memory[memory_pointer] = Filter2_Result; Filter3_Result_Memory[memory_pointer] = Filter3_Result; if(memory_pointer >= (MEMORY_SIZE - 1)) { memory_pointer = 0; } else { memory_pointer++; } // Debug if( (Filter2_Result < 8000 || Filter3_Result < 8000) && SDFMReadingCounter > 3) { ESTOP0; } if (SDFMReadingCounter > (NUM_INCORRECT_SAMPLES_AFTER_SYNC + 1)) { SDFMReadingCounter = 0; // // Write the current SDFM value to buffered DAC // // TODO: it is possible that the value below could equal 4096. Need to check that writing 4096 to // the DAC doesn't produce unexpected results. Remember 4095 is the max DAC value. // DAC_PTR[DACA]->DACVALS.all = Filter2_Result + 2048; // DAC_PTR[DACB]->DACVALS.all = Filter3_Result + 2048; DAC_PTR[DACA]->DACVALS.all = ((Filter2_Result*SDFM_SCALE_FACTOR) + 0.5)*4095; DAC_PTR[DACB]->DACVALS.all = ((Filter3_Result*SDFM_SCALE_FACTOR) + 0.5)*4095; // Reset the filter module to synchronise all 4 channels // Turn RESET LED ON/OFF to show sync point GPIO_setOutputValue43(43, 1); Sdfm_disableMFE(gPeripheralNumber); Sdfm_enableMFE(gPeripheralNumber); GPIO_setOutputValue43(43, 0); } // // Read SDFM flag register (SDIFLG) // sdfmReadFlagRegister = Sdfm_readFlagRegister(gPeripheralNumber); // // Clear SDFM flag register // Sdfm_clearFlagRegister(gPeripheralNumber, sdfmReadFlagRegister); // sdfmReadFlagRegister = Sdfm_readFlagRegister(gPeripheralNumber); /* if (sdfmReadFlagRegister != 0x0) { ESTOP0; } */ // // Acknowledge this __interrupt to receive more __interrupts from group 5 // PieCtrlRegs.PIEACK.all = PIEACK_GROUP5; // Turn OFF LED to show that ISR is finished GPIO_setOutputValue(41, 0); } // // Sdfm_configurePins - Configure SDFM GPIOs // void Sdfm_configurePins(uint16_t sdfmPinOption) { uint16_t pin; uint16_t flagMask; flagMask = GPIO_ASYNC; // Need to invert the SDFM data pins if data is Manchester encoded. This is because the delta-sigma chips use IEEE 802.3 Manchester standard // but this micro uses G.E. Thomas Manchester standard #if SDFM_MODE == MODE_2 flagMask |= GPIO_INVERT; #endif switch (sdfmPinOption) { case SDFM_PIN_MUX_OPTION1: for(pin=16;pin<=31;pin++) { GPIO_SetupPinOptions(pin, GPIO_INPUT, flagMask); GPIO_SetupPinMux(pin,GPIO_MUX_CPU1,7); } break; case SDFM_PIN_MUX_OPTION2: for(pin=48;pin<=63;pin++) { GPIO_SetupPinOptions(pin, GPIO_INPUT, flagMask); GPIO_SetupPinMux(pin,GPIO_MUX_CPU1,7); } break; case SDFM_PIN_MUX_OPTION3: for(pin=122;pin<=137;pin++) { GPIO_SetupPinOptions(pin, GPIO_INPUT, flagMask); GPIO_SetupPinMux(pin,GPIO_MUX_CPU1,7); } break; } } // // InitEPwm - Initialize specified EPWM settings // void InitEPwm(void) { uint16_t CMPC,CMPD; CMPC = 200; CMPD = 200; #ifdef CPU1 GPIO_SetupPinOptions(4, GPIO_OUTPUT, GPIO_ASYNC); GPIO_SetupPinMux(4,GPIO_MUX_CPU1,1); #endif EALLOW; // // Allows all users to globally synchronize all enabled ePWM modules to // the time-base clock (TBCLK) // CpuSysRegs.PCLKCR0.bit.TBCLKSYNC = 1; // // Setup TBCLK // (*EPWM[gPWM_number]).TBPHS.bit.TBPHS = 0x0000; // Phase is 0 (*EPWM[gPWM_number]).TBCTR = 0x0000; // Clear counter //(*EPWM[gPWM_number]).TBPRD = EPWM_TIMER_TBPRD; // Set timer period // 801 TBCLKs. (*EPWM[gPWM_number]).CMPC = CMPC; // Set Compare C value (*EPWM[gPWM_number]).CMPD = CMPD; // Set Compare D value (*EPWM[gPWM_number]).CMPA.bit.CMPA = CMPC; // Set Compare C value (*EPWM[gPWM_number]).CMPB.bit.CMPB = CMPD; // Set Compare D value // // Setup counter mode // (*EPWM[gPWM_number]).TBCTL.bit.CTRMODE = TB_COUNT_UP; // Count up (*EPWM[gPWM_number]).TBCTL.bit.HSPCLKDIV = TB_DIV1; (*EPWM[gPWM_number]).TBCTL.bit.CLKDIV = TB_DIV1; // // Set actions // (*EPWM[gPWM_number]).AQCTLA.bit.CAU = 3; // Set PWM1A on event A, up // count // // Set actions // (*EPWM[gPWM_number]).AQCTLB.bit.CBU = 3; // Set PWM1A on event A, up // count EDIS; } // Setup Diagnostic GPIO pins void GPIO_configureDiagnosticPins(void) { // // These can be combined into single statements for improved // code efficiency. // // // Enable GPIOs for uP_DIAGNOSTIC0-13 (except 6 and 7) as outputs // EALLOW; // DIAGNOSTIC0. ALSO SD2_D4, NO NOT USE /* // GpioCtrlRegs.GPBPUD.bit.GPIO62 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO62 = 1; // Load output latch GpioCtrlRegs.GPBMUX2.bit.GPIO62 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO62 = 1; // GPIO56 = output */ // DIAGNOSTIC1. ALSO SD2_D3, NO NOT USE /* GpioCtrlRegs.GPBPUD.bit.GPIO60 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO60 = 1; // Load output latch GpioCtrlRegs.GPBMUX2.bit.GPIO60 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO60 = 1; // GPIO56 = output */ // DIAGNOSTIC2. ALSO SD2_C2, NO NOT USE /* GpioCtrlRegs.GPBPUD.bit.GPIO59 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO59 = 1; // Load output latch GpioCtrlRegs.GPBMUX2.bit.GPIO59 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO59 = 1; // GPIO56 = output */ // DIAGNOSTIC3. ALSO SD2_D2, NO NOT USE /* GpioCtrlRegs.GPBPUD.bit.GPIO58 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO58 = 1; // Load output latch GpioCtrlRegs.GPBMUX2.bit.GPIO58 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO58 = 1; // GPIO56 = output */ // DIAGNOSTIC4. ALSO SD2_C1, NO NOT USE /* GpioCtrlRegs.GPBPUD.bit.GPIO57 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO57 = 1; // Load output latch GpioCtrlRegs.GPBMUX2.bit.GPIO57 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO57 = 1; // GPIO56 = output */ // uP_CH1_ACTIVE_LED GpioCtrlRegs.GPBPUD.bit.GPIO54 = 0; // Enable pullup on GPIO54 GpioDataRegs.GPBSET.bit.GPIO54 = 0; // Load output latch GpioCtrlRegs.GPBMUX2.bit.GPIO54 = 0; // GPIO54 = GPIO54 GpioCtrlRegs.GPBDIR.bit.GPIO54 = 1; // GPIO54 = output // uP_CH2_ACTIVE_LED GpioCtrlRegs.GPBPUD.bit.GPIO55 = 0; // Enable pullup on GPIO55 GpioDataRegs.GPBSET.bit.GPIO55 = 0; // Load output latch GpioCtrlRegs.GPBMUX2.bit.GPIO55 = 0; // GPIO55 = GPIO55 GpioCtrlRegs.GPBDIR.bit.GPIO55 = 1; // GPIO55 = output // uP_CH3_ACTIVE_LED GpioCtrlRegs.GPBPUD.bit.GPIO56 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO56 = 0; // Load output latch GpioCtrlRegs.GPBMUX2.bit.GPIO56 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO56 = 1; // GPIO56 = output // uP_FAULT_LED GpioCtrlRegs.GPAPUD.bit.GPIO29 = 0; // Enable pullup on GPIO29 GpioDataRegs.GPASET.bit.GPIO29 = 0; // Load output latch GpioCtrlRegs.GPAMUX2.bit.GPIO29 = 0; // GPIO29 = GPIO29 GpioCtrlRegs.GPADIR.bit.GPIO29 = 1; // GPIO29 = output // uP_HEART_LED GpioCtrlRegs.GPBPUD.bit.GPIO36 = 0; // Enable pullup on GPIO36 GpioDataRegs.GPBSET.bit.GPIO36 = 0; // Load output latch GpioCtrlRegs.GPBMUX1.bit.GPIO36 = 0; // GPIO36 = GPIO36 GpioCtrlRegs.GPBDIR.bit.GPIO36 = 1; // GPIO36 = output // DIAGNOSTIC5 GpioCtrlRegs.GPBPUD.bit.GPIO41 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO41 = 0; // Load output latch GpioCtrlRegs.GPBMUX1.bit.GPIO41 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO41 = 1; // GPIO56 = output // DIAGNOSTIC8 GpioCtrlRegs.GPBPUD.bit.GPIO43 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO43 = 0; // Load output latch GpioCtrlRegs.GPBMUX1.bit.GPIO43 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO43 = 1; // GPIO56 = output // DIAGNOSTIC9 GpioCtrlRegs.GPBPUD.bit.GPIO42 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO42 = 0; // Load output latch GpioCtrlRegs.GPBMUX1.bit.GPIO42 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO42 = 1; // GPIO56 = output // DIAGNOSTIC10 GpioCtrlRegs.GPBPUD.bit.GPIO47 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO47 = 0; // Load output latch GpioCtrlRegs.GPBMUX1.bit.GPIO47 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO47 = 1; // GPIO56 = output // DIAGNOSTIC11 GpioCtrlRegs.GPBPUD.bit.GPIO46 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO46 = 0; // Load output latch GpioCtrlRegs.GPBMUX1.bit.GPIO46 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO46 = 1; // GPIO56 = output // DIAGNOSTIC12 GpioCtrlRegs.GPBPUD.bit.GPIO45 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO45 = 0; // Load output latch GpioCtrlRegs.GPBMUX1.bit.GPIO45 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO45 = 1; // GPIO56 = output // DIAGNOSTIC13, RED LED GpioCtrlRegs.GPBPUD.bit.GPIO44 = 0; // Enable pullup on GPIO56 GpioDataRegs.GPBSET.bit.GPIO44 = 0; // Load output latch GpioCtrlRegs.GPBMUX1.bit.GPIO44 = 0; // GPIO56 = GPIO56 GpioCtrlRegs.GPBDIR.bit.GPIO44 = 1; // GPIO56 = output EDIS; } // // Set the specified user value on the specified GPIO // void GPIO_setOutputValue(uint32_t GPIONumber, uint32_t outputValue) { //TODO: change this function so that any GPIO that is configured as an output can be changed by this function // Check that the specified GPIO is configured as an output EALLOW; GpioDataRegs.GPBDAT.bit.GPIO41 = outputValue; EDIS; } // // Set the specified user value on the specified GPIO // void GPIO_setOutputValue43(uint32_t GPIONumber, uint32_t outputValue) { //TODO: change this function so that any GPIO that is configured as an output can be changed by this function // Check that the specified GPIO is configured as an output EALLOW; GpioDataRegs.GPBDAT.bit.GPIO43 = outputValue; EDIS; } // // configureDAC - Enable and configure the requested DAC module // void configureDAC(Uint16 dac_num) { EALLOW; DAC_PTR[dac_num]->DACCTL.bit.DACREFSEL = DAC_REFERENCE_VOLTAGE; DAC_PTR[dac_num]->DACOUTEN.bit.DACOUTEN = 1; DAC_PTR[dac_num]->DACVALS.all = 0; DELAY_US(10); // Delay for buffered DAC to power up EDIS; } // // InitEPwm1Example - Initialize EPWM1 values // void InitEPwm1Example() { // // Setup TBCLK // EPwm1Regs.TBCTL.bit.CTRMODE = TB_COUNT_UP; // Count up EPwm1Regs.TBPRD = EPWM1_TIMER_TBPRD; // Set timer period EPwm1Regs.TBCTL.bit.PHSEN = TB_DISABLE; // Disable phase loading EPwm1Regs.TBPHS.bit.TBPHS = 0x0000; // Phase is 0 EPwm1Regs.TBCTR = 0x0000; // Clear counter EPwm1Regs.TBCTL.bit.HSPCLKDIV = TB_DIV1; // Clock ratio to SYSCLKOUT EPwm1Regs.TBCTL.bit.CLKDIV = TB_DIV1; // // Interrupt where we will change the Compare Values // EPwm1Regs.ETSEL.bit.INTSEL = ET_CTR_ZERO; // Select INT on Zero event EPwm1Regs.ETPS.bit.INTPRD = ET_1ST; // Generate INT on 1st event } // // InitEPwm10Example - Initialize EPWM10 values // void InitEPwm10Example() { // // Setup TBCLK // EPwm10Regs.TBCTL.bit.CTRMODE = TB_COUNT_UP; // Count up EPwm10Regs.TBPRD = EPWM11_TIMER_TBPRD; // Set timer period EPwm10Regs.TBCTL.bit.PHSEN = TB_ENABLE; // Enable phase loading EPwm10Regs.TBPHS.bit.TBPHS = 0x0002; // there is a 2 cycle delay EPwm10Regs.TBCTL.bit.PHSDIR = 0x0001; // set up count mode after sync. Not needed if not in up-down count mode EPwm10Regs.TBCTR = 0x0000; // Clear counter EPwm10Regs.TBCTL.bit.HSPCLKDIV = TB_DIV1; // Clock ratio to SYSCLKOUT EPwm10Regs.TBCTL.bit.CLKDIV = TB_DIV1; EPwm10Regs.TBCTL.bit.SYNCOSEL = 0x0; // set ePWM11 to pass sync signal from ePWM1 to ePWM11 } // // InitEPwm11Example - Initialize EPWM11 values // void InitEPwm11Example() { // // Setup TBCLK // EPwm11Regs.TBCTL.bit.CTRMODE = TB_COUNT_UP; // Count up EPwm11Regs.TBPRD = EPWM11_TIMER_TBPRD; // Set timer period EPwm11Regs.TBCTL.bit.PHSEN = TB_ENABLE; // Enable phase loading EPwm11Regs.TBPHS.bit.TBPHS = 0x0002; // there is a 2 cycle delay EPwm11Regs.TBCTL.bit.PHSDIR = 0x0001; // set up count mode after sync. Not needed if not in up-down count mode EPwm11Regs.TBCTR = 0x0000; // Clear counter EPwm11Regs.TBCTL.bit.HSPCLKDIV = TB_DIV1; // Clock ratio to SYSCLKOUT EPwm11Regs.TBCTL.bit.CLKDIV = TB_DIV1; EPwm11Regs.TBCTL.bit.SYNCOSEL = 0x0; // set ePWM11 to pass sync signal from ePWM10 to ePWM12 // // Setup shadow register load on ZERO // EPwm11Regs.CMPCTL2.bit.SHDWCMODE = CC_SHADOW; EPwm11Regs.CMPCTL2.bit.SHDWDMODE = CC_SHADOW; EPwm11Regs.CMPCTL2.bit.LOADCMODE = CC_CTR_ZERO; EPwm11Regs.CMPCTL2.bit.LOADDMODE = CC_CTR_ZERO; // // Set Compare values // EPwm11Regs.CMPC = EPWM11_CMPC; // Set compare C value EPwm11Regs.CMPD = EPWM11_CMPD; // Set Compare D value } // // InitEPwm2Example - Initialize EPWM12 values // void InitEPwm12Example() { // // Setup TBCLK // EPwm12Regs.TBCTL.bit.CTRMODE = TB_COUNT_UP; // Count up EPwm12Regs.TBPRD = EPWM12_TIMER_TBPRD; // Set timer period EPwm12Regs.TBCTL.bit.PHSEN = TB_ENABLE; // Enable phase loading EPwm12Regs.TBPHS.bit.TBPHS = 0x0002; // there is a 2 cycle delay EPwm12Regs.TBCTL.bit.PHSDIR = 0x0001; // set up count mode after sync. Not needed if not in up-down count mode EPwm12Regs.TBCTR = 0x0000; // Clear counter EPwm12Regs.TBCTL.bit.HSPCLKDIV = TB_DIV1; // Clock ratio to SYSCLKOUT EPwm12Regs.TBCTL.bit.CLKDIV = TB_DIV1; // // Setup shadow register load on ZERO // EPwm12Regs.CMPCTL2.bit.SHDWCMODE = CC_SHADOW; EPwm12Regs.CMPCTL2.bit.SHDWDMODE = CC_SHADOW; EPwm12Regs.CMPCTL2.bit.LOADCMODE = CC_CTR_ZERO; EPwm12Regs.CMPCTL2.bit.LOADDMODE = CC_CTR_ZERO; // // Set Compare values // EPwm12Regs.CMPC = EPWM12_CMPC; // Set compare C value EPwm12Regs.CMPD = EPWM12_CMPD; // Set Compare D value } // // done - Function to halt debugger and stop application // void done(void) { asm(" ESTOP0"); for (;;); } // // End of file //